wcampbell

Hi all.

I'm working on my second of two assessments ( I'm a novice ).
So far I've sorted new E Tails to metal socket plates, sorted reverse polarity at cooker isolation / socket switch ( still don't understand why fridge has n't got a problem with phase in neutrals at switch! ), got all the results for the EIRC, and fitted a new CU.

My ( hopefully ) last problem concerns main bonding as follows:

Cut 30' ish of 10mm E. Tested ends and got a continuity reading of 0.02ohms.
Fitted cable in situ ( clamp at water stop, then through wall to clamp at gas mains ( cable not cut ), then back into house to CU.

About five feet of this run sees cable running parallel in conduit and wall.

Now when I carry out continuity of main bond I get -00 ohms.

I have tested with leads not nulled and get a reading 0.02 ohms lower.

Is the parallel section causing this?

I know the reading must be below 0.05ohms but surely there must be some resistance.

How will this look to the assessor?

Thanks. :nonod:
 
Have you disconnected the db end from the MET? If not there may be a parallel path??
Myself I would be thinking that that is on the limit of 10mm to meet .05

Are you testing this with a r2 lead or equivalent?
 
Thanks for your reply. Testing with Kewtec Continuity Tester with the usual red / black crocs. Main Bond is not in MET yet. 10 mm Bond tests -00ohms when disconnected from clamps.
 
You want to test it when it is all inn-situ.
Then disconnect from Met. One clip to 10mm other to r2 lead that is connected to clamp.
Then remember to remove lead resistance. If your not sure, follow the GN3 is the Best advice I can give you.
 

Reply to The never ending Assessment Installation. in the Australia area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hi, Similar'ish question to my other thread but little more info now so a different approach but sorry if duplication. UK, single phase. Just had...
Replies
0
Views
1K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock