Before we loose sight of the question don't forget that La Poste is working with a pre-installed cable and he will need to satisfy himself that the CPC meets the requirements of section 543 and table 54.1.
If its a 3 core SWA then job done - easy - but if not then it will be necessary to confirm that the CSA of the armour meets the Regulation.
If it does not then TT is the remaining option.
If its a 3 core SWA then job done - easy - but if not then it will be necessary to confirm that the CSA of the armour meets the Regulation.
If it does not then TT is the remaining option.