to kick the argument off, i always run an additional cpc other then the SWA :baby:


WHY??

In this OP's particular instance, the 4 core 16mm SWA armouring will be more than capable of providing this circuits CPC requirements!!
 
This is a table giving you an accurate means of identifying when the armouring of SWA cables will and will not comply with BS7671 requirements. As you can see, the required CSA of SWA cables only becomes suspect at cable sizes over 95mm/2core.....

These day's most SWA cables comes with thermosetting insulation (XLPE) as standard. The thermal plastic table, is still handy when assessing or dealing with older cable installations....

Make a copy of this table and you'll never have to ask again, ....If you can use the Steel Wire Armouring as your CPC!! lol!!
PLEASE NOTE.... this table does ''NOT'' relate to equivalent BONDING CSA compliance!!!


Here is an updated table that i have been using for several years now on SWA compliance, for using the armour as your CPC


Figures in brackets, ... DO NOT COMPLY.



Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.


[TABLE="class: cms_table_yiv151396182MsoTableGrid"]
[TR]
[TD]
Conductor CSA​
[/TD]
[TD="width: 118"]
Minimum CSA of SWA to meet 54G​
[/TD]
[TD="width: 118"]
CSA of armour 2 core​
[/TD]
[TD="width: 118"]
CSA of armour 3 core​
[/TD]
[TD="width: 118"]
CSA of armour 4 core​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
1.5​
[/TD]
[TD="width: 118"]
3.4​
[/TD]
[TD="width: 118"]
15​
[/TD]
[TD="width: 118"]
16​
[/TD]
[TD="width: 118"]
17​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
2.5​
[/TD]
[TD="width: 118"]
5.7​
[/TD]
[TD="width: 118"]
17​
[/TD]
[TD="width: 118"]
19​
[/TD]
[TD="width: 118"]
20​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
4​
[/TD]
[TD="width: 118"]
9.0​
[/TD]
[TD="width: 118"]
21​
[/TD]
[TD="width: 118"]
23​
[/TD]
[TD="width: 118"]
35
​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
6​
[/TD]
[TD="width: 118"]
13.6​
[/TD]
[TD="width: 118"]
24​
[/TD]
[TD="width: 118"]
36​
[/TD]
[TD="width: 118"]
40​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
10​
[/TD]
[TD="width: 118"]
22.6​
[/TD]
[TD="width: 118"]
41​
[/TD]
[TD="width: 118"]
44​
[/TD]
[TD="width: 118"]
49​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
16​
[/TD]
[TD="width: 118"]
36.1​
[/TD]
[TD="width: 118"]
46​
[/TD]
[TD="width: 118"]
50​
[/TD]
[TD="width: 118"]
72​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
25​
[/TD]
[TD="width: 118"]
36.1​
[/TD]
[TD="width: 118"]
60​
[/TD]
[TD="width: 118"]
66​
[/TD]
[TD="width: 118"]
76​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
35​
[/TD]
[TD="width: 118"]
36.1​
[/TD]
[TD="width: 118"]
66​
[/TD]
[TD="width: 118"]
74​
[/TD]
[TD="width: 118"]
84​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
50​
[/TD]
[TD="width: 118"]
56.4​
[/TD]
[TD="width: 118"]
74​
[/TD]
[TD="width: 118"]
84​
[/TD]
[TD="width: 118"]
122​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
70​
[/TD]
[TD="width: 118"]
79.0​
[/TD]
[TD="width: 118"]
84​
[/TD]
[TD="width: 118"]
119​
[/TD]
[TD="width: 118"]
138​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
95​
[/TD]
[TD="width: 118"]
107.2​
[/TD]
[TD="width: 118"]
122​
[/TD]
[TD="width: 118"]
138​
[/TD]
[TD="width: 118"]
160​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
120​
[/TD]
[TD="width: 118"]
135.3​
[/TD]
[TD="width: 118"]
(131) ​
[/TD]
[TD="width: 118"]
150​
[/TD]
[TD="width: 118"]
220​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
150​
[/TD]
[TD="width: 118"]
169.2​
[/TD]
[TD="width: 118"]
(144) ​
[/TD]
[TD="width: 118"]
211​
[/TD]
[TD="width: 118"]
240​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
185​
[/TD]
[TD="width: 118"]
208.6​
[/TD]
[TD="width: 118"]
(201) ​
[/TD]
[TD="width: 118"]
230​
[/TD]
[TD="width: 118"]
265​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
240​
[/TD]
[TD="width: 118"]
270.6​
[/TD]
[TD="width: 118"]
(225) ​
[/TD]
[TD="width: 118"]
(260)​
[/TD]
[TD="width: 118"]
299​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
300​
[/TD]
[TD="width: 118"]
338.3​
[/TD]
[TD="width: 118"]
(250) ​
[/TD]
[TD="width: 118"]
(289)​
[/TD]
[TD="width: 118"]
(333)
​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
400​
[/TD]
[TD="width: 118"]
403.9​
[/TD]
[TD="width: 118"]
(279) ​
[/TD]
[TD="width: 118"]
(319)​
[/TD]
[TD="width: 118"]
467
​
[/TD]
[/TR]
[/TABLE]



Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.


[TABLE="class: cms_table_yiv151396182MsoTableGrid"]
[TR]
[TD]
Conductor CSA​
[/TD]
[TD="width: 118"]
Minimum CSA of SWA to meet 54G​
[/TD]
[TD="width: 118"]
CSA of armour 2 core​
[/TD]
[TD="width: 118"]
CSA of armour 3 core​
[/TD]
[TD="width: 118"]
CSA of armour 4 core​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
1.5​
[/TD]
[TD="width: 118"]
3.4​
[/TD]
[TD="width: 118"]
16​
[/TD]
[TD="width: 118"]
17​
[/TD]
[TD="width: 118"]
18​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
2.5​
[/TD]
[TD="width: 118"]
5.7​
[/TD]
[TD="width: 118"]
17​
[/TD]
[TD="width: 118"]
19​
[/TD]
[TD="width: 118"]
20​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
4​
[/TD]
[TD="width: 118"]
9.0​
[/TD]
[TD="width: 118"]
19​
[/TD]
[TD="width: 118"]
21​
[/TD]
[TD="width: 118"]
23​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
6​
[/TD]
[TD="width: 118"]
13.6
​
[/TD]
[TD="width: 118"]
22​
[/TD]
[TD="width: 118"]
23​
[/TD]
[TD="width: 118"]
36​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
10​
[/TD]
[TD="width: 118"]
22.6​
[/TD]
[TD="width: 118"]
26​
[/TD]
[TD="width: 118"]
39​
[/TD]
[TD="width: 118"]
43​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
16​
[/TD]
[TD="width: 118"]
36.1​
[/TD]
[TD="width: 118"]
41​
[/TD]
[TD="width: 118"]
44​
[/TD]
[TD="width: 118"]
49​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
25​
[/TD]
[TD="width: 118"]
36.1​
[/TD]
[TD="width: 118"]
42​
[/TD]
[TD="width: 118"]
62​
[/TD]
[TD="width: 118"]
70​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
35​
[/TD]
[TD="width: 118"]
36.1​
[/TD]
[TD="width: 118"]
62​
[/TD]
[TD="width: 118"]
70​
[/TD]
[TD="width: 118"]
80​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
50​
[/TD]
[TD="width: 118"]
56.4​
[/TD]
[TD="width: 118"]
68​
[/TD]
[TD="width: 118"]
78​
[/TD]
[TD="width: 118"]
90​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
70​
[/TD]
[TD="width: 118"]
79.0​
[/TD]
[TD="width: 118"]
80​
[/TD]
[TD="width: 118"]
90​
[/TD]
[TD="width: 118"]
131​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
95​
[/TD]
[TD="width: 118"]
107.2​
[/TD]
[TD="width: 118"]
113​
[/TD]
[TD="width: 118"]
128​
[/TD]
[TD="width: 118"]
147​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
120​
[/TD]
[TD="width: 118"]
135.3​
[/TD]
[TD="width: 118"]
(125) ​
[/TD]
[TD="width: 118"]
141​
[/TD]
[TD="width: 118"]
206​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
150​
[/TD]
[TD="width: 118"]
169.2​
[/TD]
[TD="width: 118"]
(138)
​
[/TD]
[TD="width: 118"]
201​
[/TD]
[TD="width: 118"]
230​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
185​
[/TD]
[TD="width: 118"]
208.6​
[/TD]
[TD="width: 118"]
(191) ​
[/TD]
[TD="width: 118"]
220​
[/TD]
[TD="width: 118"]
255​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
240​
[/TD]
[TD="width: 118"]
270.6​
[/TD]
[TD="width: 118"]
(215) ​
[/TD]
[TD="width: 118"]
(250)​
[/TD]
[TD="width: 118"]
289​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
300​
[/TD]
[TD="width: 118"]
338.3​
[/TD]
[TD="width: 118"]
(235) ​
[/TD]
[TD="width: 118"]
(269)​
[/TD]
[TD="width: 118"]
(319)
​
[/TD]
[/TR]
[TR]
[TD="width: 118"]
400​
[/TD]
[TD="width: 118"]
451.0​
[/TD]
[TD="width: 118"]
(265) ​
[/TD]
[TD="width: 118"]
(304)​
[/TD]
[TD="width: 118"]
452
​
[/TD]
[/TR]
[/TABLE]

​



Read more: http://www.electriciansforums.net/e...n-we-use-armour-swa-cpc-11.html#ixzz2BdTJA1PD COPIED from post #155 of this thread
 
Whilst the table Engineer54 has given is a good reference bear in mind that the SWA CSA will vary from manufacturer to manufacturer
 
Disconnection times. Zs, fault current , thermal constraints, short circuit protection. Look at k factors. 17 th Ed and blue book (design guide) for swa info.
 
Whilst the table Engineer54 has given is a good reference bear in mind that the SWA CSA will vary from manufacturer to manufacturer

Really, ....well that would be news to the BSI, which give minimum dia CSA for the individual steel wires relating to the size of the conductors and mechanical protection afforded.... So in essense, could exceed the table's reference CSA but wont be lower than them!!!
 
So in essense, could exceed the table's reference CSA but wont be lower than them!!!

Thats what I was getting at because some of the non compliant cables are only fractionally non-compliant, picking a 'better' manufacturer could save on other costs

Doesn't the table also rely on certain assumptions, using the adiabatic could result in a lower SWA CSA being required for specific cases. eg. long runs using larger conductors to overcome Voltage drop.
 
Last edited by a moderator: