E
Engineer54
to kick the argument off, i always run an additional cpc other then the SWA![]()
WHY??
In this OP's particular instance, the 4 core 16mm SWA armouring will be more than capable of providing this circuits CPC requirements!!
to kick the argument off, i always run an additional cpc other then the SWA![]()
Whilst the table Engineer54 has given is a good reference bear in mind that the SWA CSA will vary from manufacturer to manufacturer
So in essense, could exceed the table's reference CSA but wont be lower than them!!!