Sintra
Thanks to all who responded productively, the supply is 3 phase 420v fused by two 100a and one 60a this is fed Into ryefield board 5 way which is feeding shop and 2 flats by of 5 60a fuses. See pictures attached. This is then fed using armoured cable to db. Have done continuity tests live phases to earth and neutral no fault found. Insulation resistance is 675m ohm and passes fine. When I fit l1 fuse in ryefield db works fine, however if I fit l2 fuse and test it blows fuse l1 and l2 but the flats are unaffected as they are fed direct off supply. Any productive help will be appreciated. By the way phases are correct and even if they would not that should not blow fuse on ryefield.
What about an IR and continuity test between phases. What way is the SWA glanded into the bottom of the ryefield.