Currently reading:
TNCS - USING NEUTRAL AS EARTH IN BOARD
Discuss TNCS - USING NEUTRAL AS EARTH IN BOARD in the UK Electrical Forum area at ElectriciansForums.net
Im travelling abroad to a country that has no earthing arrangement and my friend would like me to do a bit of work on his house. My question is Whether or not i could create a link between the Neutral and Earth bar to create a tncs system.
I know it sounds strange but i have just been thinking for the past couple of days how they do it here in the uk. They do the same thing for tncs systems a link between neutral and earth.
Could someone shine some light on the subject as to why it cannot be done and how it can be done here then?
P.s i know a earth rod can be hit into the ground but want to explore all options.
If RCDs are used, and you create the link from the neutral bar(s) to earth (as in your OP), the RCD then will not see any fault current and will fail to operate, because any earth fault is directed back down neutral before it passes through the RCD.
Just a minor point,but the OP never mentioned what type of supply we were discussing,could be national,local or private generation...will affect any earthing decisions directly.
RCDs don't detect fault current, they detect imbalances between Line and Neutral.
The Neutral Earth link is placed up stream from any RCD, which prevents any earth Fault Current from bypassing the RCD via the Neutral.
To the OP, with TN-C-S in this country, a single conductor is used to carry Neutral and Earth Fault Currents. Not two conductors joined together.
The link between Neutral and Earth is put there to allow the installation earth a path back to the Transformer.
What you suggest would work, and if were only a single installation with the link, it would be unlikely to have any adverse affect on the distribution system.
The OP specifically said the link would be in the bus bar, which on the boards I've worked with would be before any RCD. That way fault current returns through the neutral and through the RCD as normal current would, and the RCD would not operate.
No thats not what i mean , forgot war and all that. Why is it that a in one house a tncs system here can be connected to neutral but in another house it cant?
because where PME is provided, the supply has the N (star point) reliably earthed at several points along it's route. therefore, it's maintained at ground potential. best option is to TT it with RCD for fault protection, as wilko stated .
Yes, creating the link at the busbar, or anywhere down stream from the RCD would cause the RCD to trip whenever power was used.
Okay, so the scenario in the OP was that a link was made between the earth and neutral bus bars. This is my interpretation of that, as depicted by the purple line. (Apologies about the Paint job, not quite Richard Burns spec).
So current flows through the line through the RCD, and out on the first circuit. There's a fault, and it returns via the earth path. The earth path is linked to neutral before it passes through the RCD, and the current then passes through the neutral via the RCD. The RCD wouldn't see a fault and doesn't operate.
You won't get to the fault stage, as the RCD will operate as soon as any power is used.
Some of the return current will return to the power supply via the earth instead of via the neutral.
The RCD will see the imbalance between the Line and neutral and trip.
What earth? There is no earth, it has been linked to neutral to create a bodged TNCS
You've only got to think of the scenario of wrong neutral leg to wrong neutral bar or when you're working on a circuit switched off at the board but neutral not removed, so easy to trip if neutral and earth touch. The amount of imbalance needed through the RCD coils is minuscule to cause a trip. No way would the install be a happy install if @hightower 's scenario was attempted.
I'd argue quite the contrary - it would be too happy, and would render the RCD completely useless.
It's electrickery, it knows more than us! We're just wire monkeys! I understand your passion though - we need a "myth buster"
Hi - not wishing to step into a hole, but would not the luckless chap be standing on the earth and the earth fault current flow through him? This would unbalance the RCD in the usual way, if it had ever been able to stay on line to begin with as per Spin #45 and Rpa #47 thoughts.
Do it, you know you want to :)
It is my intention but for it to be a scientific thingy you would have to isolate the board from all sources of earth which may be impossible, you have the earthing conductor, bonds and all those circuits linked to extraneous parts like water heaters, boilers etc.. to lose. I see defeat before I start.
The experiment has taken place at a board with the earthing conductor disconnected and none of the circuits in contact with extraneous parts. With a link across the earth and neutral bars the board functions, as soon as you reintroduce the earth the rcd trips.
Reply to TNCS - USING NEUTRAL AS EARTH IN BOARD in the UK Electrical Forum area at ElectriciansForums.net