Should I be getting a dead short at DB on ohms scale when connecting leads of ohm meter across neutral bar and earth bar or would that only apply to TNCS??
 
What reading are you getting and with what are you measuring it with.
Meggar 1720 mft...
My "issue" is I'm trying to figure out if I should or should not be getting a dead short.
I have a DB with dual supplies(A+B)

On A supply on ohms scale I am getting a dead short(0.03)ohms
On B supply I am showing open circuit.

They are fed from 2 different substations(both containing H.V transformers)

I'm thinking maybe I shouldn't be getting a short.And I maybe have a neutral earth fault,but due to only having a 3 pole switch I cant isolate the neutral unless I can get access to LV switchboards to remove neutral link on mccb
I was just trying to figure out generally if I should be expecting to see dead short.The cable run is just about 30M.
 
Ok, with TNS I would not expect to see 0.03 Ohms N-E. What size cables? And when you say 30m run - from where to where please?
 
Last edited by a moderator:
Hi,bud,Could do with less of the dead short,as myself and six of my pals,are feeling the lack of diversity treatment ;)
 
Ok, with TNS I would not expect to see 0.03 Ohms N-E. What size cables? And when you say 30m run - from where to where please?
From DB to HV/LV substation 70mm cable (my understanding of tns is the neutral is derived from the earthed star point on the secondary windings .I'm wondering has the earth been omitted to the neutral.)
 
Assuming 70mm conductor size for both N, at 20C the resistance for 30m is about 0.024Ohms. And a 37m run would be 0.03Ohms. Unless I've made a no-coffee-yet mistake.
 
Last edited by a moderator:
Therefore the neutral of the non operational supply (B) is probably not connected to your live supply as this would mix the two systems of the supply transformers.
Both supplies are operational..voltage to earth is 240 on both systems..There is some info about earthing neutrals through impedences(fig 44.1)and section 442 .not too clear to me..
Incidently when I measure on megohm scale I am showing 0.00
 
Hi,what is the set-up,regarding the two supply transformers,and what is feeding them?
Hi.I cant really comment.I will need to investigate further.The complex has 5 sets of HV/LV Transformer rooms(Subs) (Times 2 :A+B) I believe there are two independant 11,000volt ring mains.They wont let us doe_heads in to the substations.
So I could still be looking at either a neutral earth fault or a missing earth link on neutral...I've been trying to read up but it appears the HV earth &LV earthed neutral can either be separate or common or through an impedence..
 
Hi,it may be beneficial,to find the spec on the supply characteristics,which should be available to yourself.

Maybe not in this case,but some installations can have dual intakes,TN-S and PME,and there are very specific requirements,regarding separation distances,bonding,removable links,etc.
 
Hi,it may be beneficial,to find the spec on the supply characteristics,which should be available to yourself.

Maybe not in this case,but some installations can have dual intakes,TN-S and PME,and there are very specific requirements,regarding separation distances,bonding,removable links,etc.
Ok thanks..Substations arn't really my game.,but I'll try and get more info
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
TNS
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
31

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
mrloy99,
Last reply from
mrloy99,
Replies
31
Views
3,370

Advert

Back
Top