Yes,and?Well a dead short is little or no resistance.
Meggar 1720 mft...What reading are you getting and with what are you measuring it with.
Thanks for your reply but I thought I made that pretty clear in the titleOk, first question is what is the installation means of earthing?
Sorry Peg(or porg in a morgue if you prefer)Hi,bud,Could do with less of the dead short,as myself and six of my pals,are feeling the lack of diversity treatment![]()
Yep good for you. Best wishes.Thanks for your reply but I thought I made that pretty clear in the title
From DB to HV/LV substation 70mm cable (my understanding of tns is the neutral is derived from the earthed star point on the secondary windings .I'm wondering has the earth been omitted to the neutral.)Ok, with TNS I would not expect to see 0.03 Ohms N-E. What size cables? And when you say 30m run - from where to where please?
Theres a fault on a circuit yes.Its a new installation.About to be handed overHi,was there a reported fault,which instigated your testing?
A couple of months ago yes when it was first powered up..As far as I remember it was around 0.07..(quite big job over a hundred DBs so not sure)Have you carried out a Ze at the boards.
No continuity on an accessory fault traced to defective modular kit.faulty circuit disconnected (I think)unless labled wrongly.not confirmed yet.What is the nature,of the fault?
One or the other...manual changeover.Are both A & B supplies used at the same time or is it a duty / standby situation?
Thank you...For the Neutral Earth loop on the installation you describe the 0.03Ω sounds about right (as Wilko has just said!)
So the A installation sounds correct but the B does not.
View attachment 39394
Therefore the neutral of the non operational supply (B) is probably not connected to your live supply as this would mix the two systems of the supply transformers.One or the other...manual changeover.
Thank you...
Both supplies are operational..voltage to earth is 240 on both systems..There is some info about earthing neutrals through impedences(fig 44.1)and section 442 .not too clear to me..Therefore the neutral of the non operational supply (B) is probably not connected to your live supply as this would mix the two systems of the supply transformers.
Hi.I cant really comment.I will need to investigate further.The complex has 5 sets of HV/LV Transformer rooms(Subs) (Times 2 :A+B) I believe there are two independant 11,000volt ring mains.They wont let us doe_heads in to the substations.Hi,what is the set-up,regarding the two supply transformers,and what is feeding them?
Ok thanks..Substations arn't really my game.,but I'll try and get more infoHi,it may be beneficial,to find the spec on the supply characteristics,which should be available to yourself.
Maybe not in this case,but some installations can have dual intakes,TN-S and PME,and there are very specific requirements,regarding separation distances,bonding,removable links,etc.