Snapester
Whats is the no no with hager board just out of interest, i've not heard it?
He has obviously decided to use the RCD unit to provide isolation over the 3m distance although i'm not sure if that breaker is DP, and then fed the following consumer unit with the 16mm T&E to the new CU.
Wouldn't the 40a RCD unit provide overcurrent protection for the 16mm T&E CU supply, although i agree that the diversity for the 2nd CU is probably incorrect. But surely if the cable is protected via the 40a RCD then this should prevent cable overload? And by the look they haven't overloaded it so far?
Not saying it isn't a shambles but does it contravene regs?
He has obviously decided to use the RCD unit to provide isolation over the 3m distance although i'm not sure if that breaker is DP, and then fed the following consumer unit with the 16mm T&E to the new CU.
Wouldn't the 40a RCD unit provide overcurrent protection for the 16mm T&E CU supply, although i agree that the diversity for the 2nd CU is probably incorrect. But surely if the cable is protected via the 40a RCD then this should prevent cable overload? And by the look they haven't overloaded it so far?
Not saying it isn't a shambles but does it contravene regs?