I have a 37KW motor and need to replace some burnt out 35mm2 tri rated cable(loose connection). I’ve looked at 25mm2 Tri rated cable the data sheet says it’s current carrying capacity is 136amps. The lengths will be 0.5m.Is there any other consideration I should take into consideration? It will be in trunking with the control circuit. Do I need to apply any de rating factors?
Thanks guys
Thanks guys
supervisor told me to run it in 25 but my question to him was why it was 35 in the first place. His response was that the cable can take 136amps so it’s all good. But with derating as you’ve stated it could possibly not be protected against overload. I guess this isn’t a question of BS7671 and more 60204. However I’m still not clear on these calculations.