Of the top of me bonce, assuming a newly installed circuit.
Visual checks (usually done during construction if working alone).
End to end continuity of conductors, using either R1+R2 method or wandering lead method (favour the first as you'll get polarity as a side effect).
Insulation resistance testing of conductors for final circuits
Polarity checks.
Then on to live testing:
Live Polarity Test.
Ze, current tests, Zs.
Then on to RCD/RCBO tests
and finally functional testing.
In practice for an existing installation you'd normally check Ze, PSSC etc
you missed out the wet finger test! :crazy:
)conductors when doing continuity.