The other day meter read 400ms and it never tripped,but today on 1x it tripped and 5x read 25v at a socket outlet.

If your meter is set at 25v touch voltage, it will stop the test if you get close to that voltage.

150mA x 145 ohms is pretty close at 21.75v.
 
i'd also be looking at trying to get the Ze down with an additional rod. 2-3 screwed together for depth.
 
Trouble is Tel unless he can confirm the tester works the actual impedance reading he had may be wrong, the 145 ohms maybe 20 ohms LOL
 
54 posts in for a Zs/Ze which complies and meets disconnection times,or would if the RCD was functional....and an OP who thinks the max Zs for the OCPD applies on a TT......God 'elp us,and God 'elp the client if this is an EICR.
 
Hi,

Don't forget lads, it is Friday and we always have some gooduns turn up. I especially like the one where the reading is higher than the OSG!