How would TN-S work if there’s no reference to earth?

It's not TT due to the fact that the reference point isn't transferred through the mass of earth. I.e from a rod at a house to the DNO tx.

A generator with a Rod is TN-S as in all intents and purpose it can be treated as a transformer secondary. Albeit with a low potential earth fault current.

You wouldn't rod a genny and then run phases to whatever you were feeding without a CPC just to install a second rod there. (This instance it would be TT)
 
Just looking at the second part of this reg with the statement " The neutral point or the midpoint of the power supply system shall be earthed. If the neutral point or midpoint is not available or not accessible, a line conductor shall be earthed"
My question is... I assume they are talking about the connection at the transformer sub station and if so why did they feel the need to add this, as I haven't seen it there before now?
Its all part of the wiring regs poking their nose into DNO matters. Just disregard it.
 

Reply to TT system - Reg 411.5.1 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock