If all the circuits were RCBO protected my money is on only 1 cct tripping (the faulty one) even with the bonding reconnected !
 
Thanks Lucien and others for your advice much appreciated. I do follow what you say and also what you say about fault current bypassing the RCD.

When I go back I'll bypass the RCD altogether for test purposes and put clamp meters on every part of the isolated circuit to see what's going on including earths . I've done hundreds of RCD trips and this is the only one in nearly fifteen years I can't see an explanation for as there is no other effective connection to earth bar the CPC in the cable

All my test gear is properly calibrated too so I trust my readings. I'll do differentials and all other tests thoroughly later.

I'll end up lying awake tonight with obscure routes to earth going round my head.
 
Would be nice to find out what the fault is (when you eventually find it) so post it up
 
Hi there just working in friend of the family's place supplied by tt system will it past a test and inspection with the board being is isolated by a 100 ma rcd or does it need a main switch within the board

thanks
 
what other purpose can a sombrero possibly serve?
 
Shower is brand new and also passed the IR test after use. It was good and hot too as after initially getting it all working as flowrate was so very low and the thermal cut out came in.

I had my money on the shower too on the way to the job but absolutely fine.

Did you IR test the shower unit with it turned on, ie. IR tested the internal heating elements?
 
Obviously as a dead test but yes. Joined L+N and tested at 500v to earth point inside shower after use and so hot. Cut out had reset itself by then too. Reading >200Mohm so fine.

Or do you mean straight forward resistance test between L / N of element which I'd expect to be around the 7ohms region?
 
could it be a high resistance on the neutral causing an imbalance.
possibly a loose connection either at cu or meter position beside cu or next door.
 