So the elements have been overheated and cutout due to thermal trip ... it could be the fact that the elements took some damage that has since cleared ... cheap shower if it dosn't have a basic flow/pressure switch.. but you get what you pay for.
 
could it be a high resistance on the neutral causing an imbalance.
possibly a loose connection either at cu or meter position beside cu or next door.


Any loose connections are not my end as I've tested for all that. A quick pointy ended screwdriver is one of the easiest tests.

If there's a neutral fault next door it could throw a high voltage through the earth loop assuming it isn't bonded very well to any another PME along the other houses to rescue it. We're the end house so in theory, it's only next door that could be at fault, assuming it's possible to affect it that is, which is under debate.

Let me say this. Looking at the standard of houses and tenants along the route, I doubt many decent sparks have been inside any of them. The ones that did venture inside were probably got rid of as anything north of fifty quid for a full test, remedial and cert was laughed out of the front door so there is no guarantee anything within the nearest four houses is safe.
 
So the elements have been overheated and cutout due to thermal trip ... it could be the fact that the elements took some damage that has since cleared ... cheap shower if it dosn't have a basic flow/pressure switch.. but you get what you pay for.

The shower is a Galaxy Aqua 1000. Not the best but not the worst either. Brand new and working perfectly as soon as the earth bond to next door is removed. This model has a pressure switch too.

But you make a point worth noting.
 
Not going to go into what's causing the problem at this stage, as you have some things to clear up and check out on your return.

What i can't make out, is if PME is obviously available on this street. why are there still TT systems in place?? 88 ohms is better than 200 ohms, but it sure isn't better than < 0.35 ohms. So no matter what the eventual cause of this problem is, I'd strongly advise this householder to have the supply PME'd....
 
quote_icon.png
Originally Posted by Lucien Nunes Can you explain how it would do that?



I see that you're being diplomatic here. I've used the same sort of response myself from time to time. A bit more subtle than getting into a

What I meant was, I can see a possible (albeit far-fetched) mechanism, where a loose N connection at the CU causes transients across the N-E capacitance of the installation when heavily loaded. I think it's unlikely as the flickering and probable overheating would have come to the OP's attention, and also he states that the trip occurs the moment the shower is switched on, every time. However a poor connection in next door's neutral seems like a red herring, and was curious as to the suggested explanation for that...
 
I can confirm there is no flickering or any loose neutrals my side.

Next line of inquiry will be change of RCD to a known reliable one plus a box full of clamp meters testing an isolated circuit testing at every point possible.

If so much as a milliamp escapes I'll be onto it.

Edit: I might even put an ammeter in series with the water bond and test the direction of current if something shows up.
 
Excellent, keep us posted!

Also, some pics would be good, I don't expect they'll reveal anything but it's nice to see what you can see, rather than our own imaginary pictures that we concoct as the story unfolds.
 
^^ This. You need to see the set up Eng. They still have what passes for normal streets wired by overhead telegraph pole with transformers nailed to them.

Nothing remotely strange about that.... You'll find that most if not all overhead PME systems are ''True PME'' and not TNC-S!!
 
And lots of pictures of everything!!!



edit:

Lucien's already said that, but just to emphasise the point! :-) They do make things a lot easier.
 
Last edited by a moderator: