On a side note. Instantaneous in current liming like a fuse? As I understand it a fuse begins to melt as soon as it gets hot, while a solenoid must saturate, pull in, and then wait to unlatch with an arc which takes time to extinguish.
I know that RK low peak fuses tend to reduce arc flash to a big degree relative to instantaneous tripping of molded case circuit breakers and power circuit breakers .
Yes, although the I^2t let through is very much more than a fuse will give; for the very reasons you state
I do not like MCB - fuses are so much better for protecting circuits, coordinating with each other and providing an overall better system.
Unfortunately fuses are inconvieniant - so MCB end up being king!
[automerge]1591982378[/automerge]
Ill take your word for it. That if it means if means loop impedance requirements are met than the CPC will always be greater than what the adiabatic method would calculate out to be when dealing with T&E.
Slightly more to it than that, firstly you have to ensure the protection operates within the time limits (which is via selection of correct MCB and the Zs {loop impedance} requirements)
Then, secondly that the CPC is larger than the minimum size given the MCB type, class, and fault level.
So if I have a fault level less than 3kA, a 20A class 3 B type MCB then:
1) The Zs must be less than 1.1ohm (at the time of install - i.e. when cold)
2) The CPC must be bigger than 1.5mm^2
1) can be found from table B6 in the OSG
2) can be found from table B7 in the OSG
In which case standard 2.5mm^2 T&E can be used
Change the fault level to between 3kA and 6kA then again from B6 & B7:
1) The Zs must be less than 1.1ohm (at the time of install - i.e. when cold)
2) The CPC must be bigger than 2.5mm^2
- In this case you can't used standard T&E , and is often the case for industrial sites where the CPC has to be the same size as the live conductors
(of course you would also check for volt drop, cable rating due to installation method etc.)
Above 6kA fault level then you need the manufacturers data and have to calculate manually (although there are other tables available - just not in the standard stuff)
[automerge]1591982770[/automerge]
Yes, although the I^2t let through is very much more than a fuse will give; for the very reasons you state
I do not like MCB - fuses are so much better for protecting circuits, coordinating with each other and providing an overall better system.
Unfortunately fuses are inconvieniant - so MCB end up being king!
[automerge]1591982378[/automerge]
Slightly more to it than that, firstly you have to ensure the protection operates within the time limits (which is via selection of correct MCB and the Zs {loop impedance} requirements)
Then, secondly that the CPC is larger than the minimum size given the MCB type, class, and fault level.
So if I have a fault level less than 3kA, a 20A class 3 B type MCB then:
1) The Zs must be less than 1.75ohm (at the time of install - i.e. when cold)
2) The CPC must be bigger than 1.5mm^2
1) can be found from table B6 in the OSG
2) can be found from table B7 in the OSG
In which case standard 2.5mm^2 T&E can be used
Change the fault level to between 3kA and 6kA then again from B6 & B7:
1) The Zs must be less than 1.75ohm (at the time of install - i.e. when cold)
2) The CPC must be bigger than 2.5mm^2
- In this case you can't used standard T&E , and is often the case for industrial sites where the CPC has to be the same size as the live conductors
(of course you would also check for volt drop, cable rating due to installation method etc.)
Above 6kA fault level then you need the manufacturers data and have to calculate manually (although there are other tables available - just not in the standard stuff)
So unfortunately it timed out and I can't edit it!
I changed the MCB to 20A so I could use the 2.5mm^2 T&E to illustrate the differance, but couldn't change the Zs to 1.75 from 1.1 ohm as it timed out!!