IEC 60364-5-54 states that phase conductors 16mm2 and smaller require a CPC of the same size, over 16 to 35mm2 a 16mm2 CPC and over 35mm2 a half size CPC is required.

My questions is why am I seeing catalogs with harmonized twin and earth with reduced size CPCs over 2.5mm2? And why doesn't the half size rule kick in when wire is over 4mm2 instead of 16mm2?
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members

Ian1981

-
Mentor
Arms
Esteemed
A cpc can be either sized to table 54.7 in bs7671 or calculated using the adiabatic equation. An equal sized cpc to the line conductors is rarely required, especially when current limiting ocpd’s such circuit breakers and fuses are used.
I believe in Ireland, the twin and cpc cables have equal sized conductors as is now required by their regulations.
Only 1mm2 twin and earth has the same sized cpc, 1.5 has a 1mm cpc, 2.5 a 1.5 mm cpc, 4mm a 1.5mm cpc, 6mm a 2.5mm cpc ,10mm a 4mm cpc and 16mm a 6mm cpc.
 
Last edited:
  • Thread Starter Thread Starter
  • #3
Interesting way of doing it. Why do some countries use a full size CPC others go one or two sizes smaller?
 

GBDamo

-
Supporter
Interesting way of doing it. Why do some countries use a full size CPC others go one or two sizes smaller?
Different electricity, I think.

As soon as all our Chinese nukes are online we will have to revisit our CPC requirements and bring them in line with Chinese regs, I think.
 

Ian1981

-
Mentor
Arms
Esteemed
Interesting way of doing it. Why do some countries use a full size CPC others go one or two sizes smaller?
The only reason I can think is cost to manufacture the cable, as the regulations don’t bound you to use a cpc the same size, it’s not required to produce twin and cpc cables that have conductors all the same size.
 

Risteard

-
Arms
Esteemed
I believe in Ireland, the twin and cpc cables have equal sized conductors as is now required by their regulations.
5th September 2017 was the cut-off date for the old-style T&E. (It should be noted that there weren't identical cpc sizes to British Standard cable before that, however. As an example 16mm^2 T&E had to have a 10mm^2 (rather than 6mm^2) cpc; 10mm^2 had a 6mm^2 (not 4mm^2) cpc etc.)
 

davesparks

-
Mentor
Arms
Esteemed
Interesting way of doing it. Why do some countries use a full size CPC others go one or two sizes smaller?
Because some countries like to waste the rapidly dwindling natural resources of this planet.
Or maybe they just don't trust the people installing the cables to understand the relatively simple calculations required.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
I think the only types of general light duty installation cable that have a bare CPC are UK T+E and USA NM and their derivatives, of which the NM has equal CPC but T+E CPC is reduced above 1.0mm². I think I have seen a couple of types of reduced, bare CPC T+E of indeterminate origin in North Africa with an approximation to US colours, but it might have been equal.

Australian TPS, Russian ВВГ-Пнг and its derivatives, and all the common European circular cables like NYM-J and KH05-VV, and other kinds of flat cable such as NYIF share with the Irish cable the equal-sized, insulated CPC.

There are probably many historical factors that led to the present-day choice of round vs. flat, bare vs. insulated, equal vs. reduced CPC; just as there are with choices of voltage, frequency, plug designs etc. So I don't think it's as clearcut as one country having a 'better' cable specification than another through engineering design alone.
 
  • Thread Starter Thread Starter
  • #11
US NM-B has a full size CPC for 2.08mm2, 3.31mm2 and 5.26mm2 live and neutral.


Here is the Canadian version, reduced size CPC for 12 and 10 gauge live and neutral:

https://www.mysouthwire.com/medias/...2JiNDI0NDZkYTc0MzM1MDUwNzc4Y2M2ZjgwOGQ3M2JkNg

The thing is the IEC-60364 seems to be most conservative in that they advocate for a full size CPC all the way up to 16mm2... something that I don't think any country does except those that use 60364 without amending it.
 
We choose cost over safety we then have to waste time doing doing direct Zs tests etc to make sure the CPC is satisfactory.

There is a youtube video about adiabatic equation, think it's Italian.
 
  • Thread Starter Thread Starter
  • #13
The adiabatic equation is scary to be honest... I thought 2.08mm2 on a 40 amp breaker wad bad :oops: The IEC seems to insinuate its better for TT earthing. And I could understand that, especially since TT earthing tends to be used in developing countries where cost is critical.

I'm trying to find the k factor for AWG wire sizes just so I can compare our CPCs.
 

davesparks

-
Mentor
Arms
Esteemed
We choose cost over safety we then have to waste time doing doing direct Zs tests etc to make sure the CPC is satisfactory.

There is a youtube video about adiabatic equation, think it's Italian.
Why do you think Zs testing is a waste of time?
Whatever size CPC you install it is still an essential test to confirm the requirements of ADS have been met.
 
Why do you think Zs testing is a waste of time?
Whatever size CPC you install it is still an essential test to confirm the requirements of ADS have been met.
Waste time was a bit harsh but the money we save will eventually be lost to testing, where as if we used the same size CPC we would only need to test PEFC/Ze at origin like we do PSCC.
 

Megawatt

-
Arms
The adiabatic equation is scary to be honest... I thought 2.08mm2 on a 40 amp breaker wad bad :oops: The IEC seems to insinuate its better for TT earthing. And I could understand that, especially since TT earthing tends to be used in developing countries where cost is critical.

I'm trying to find the k factor for AWG wire sizes just so I can compare our CPCs.
Cookie I’ll say this up to 30 amps the neutral and ground has to be the same size, after that you can derate the ground only. As far as the neutral goes after 200 amps the you can derate the neutral 70% of the ungrounded conductors. I just can’t understand why we don’t keep the neutral the same size as the ungrounded conductors which would go a long way as far as harmonics are considered. I myself do not derate neutrals because of the manufacturing plants that I work in have all kinds of problems with VFD’s, electronic ballasts, etc.
 
  • Thread Starter Thread Starter
  • #17
Cookie I’ll say this up to 30 amps the neutral and ground has to be the same size, after that you can derate the ground only. As far as the neutral goes after 200 amps the you can derate the neutral 70% of the ungrounded conductors. I just can’t understand why we don’t keep the neutral the same size as the ungrounded conductors which would go a long way as far as harmonics are considered. I myself do not derate neutrals because of the manufacturing plants that I work in have all kinds of problems with VFD’s, electronic ballasts, etc.
Yup and yup.

Though if you have to upsize the phase conductors for voltage drop you must also do so with the EGC.
 
  • Thread Starter Thread Starter
  • #18
Why do you think Zs testing is a waste of time?
Whatever size CPC you install it is still an essential test to confirm the requirements of ADS have been met.

I like the way you think :)
 

pc1966

Arms
Esteemed
Waste time was a bit harsh but the money we save will eventually be lost to testing, where as if we used the same size CPC we would only need to test PEFC/Ze at origin like we do PSCC.
Testing is not just confirming the calculations you know...
Post automatically merged:

I'm trying to find the k factor for AWG wire sizes just so I can compare our CPCs.
The k-factor is about the material (copper, aluminium, steel) and acceptable temperature rise (so typically a few small variariation based on PVC, XLPE, etc). The units might vary, but so long as you work things out in one consistent standard (e.g. mm2) and then convert back in to equivalent AWG it is fine.

Actually that is a very good reason why SWG and AWG as cable sizing are pants - they have no direct usable value for calculation or comparison of size!
Post automatically merged:

As others have said, the size is purely down to regulations.

The CPC does not normally carry current so it only has to be big enough for fault clearing, but the historical and regional approach to sizing that may have varied massively depending on the type of circuit protection device and the assumed skill levels of those designing / installing the circuits.

In the UK at least you always had to size the OCPD for the thinnest of cables on the circuit for normal overload protection, so immediately under fault conditions (which a current to the CPC is) you would be looking at rapid disconnection and so the I2t ought to be low enough for a reduced-size CPC. But you also have to consider the mechanical aspect of CPC strength, termination and corrosion, etc, which is (I think) the reason for various lower limits on CPC size that you see in the BS regs.

In other regions they may have had different rules on circuit OCPD selection, or less rigorous guidance for installed length, etc, that resulted in a mandate for the same CPC size to manage the fault-clearing safely.
 
Last edited:
  • Thread Starter Thread Starter
  • #20
Actually that is a very good reason why SWG and AWG as cable sizing are pants - they have no direct usable value for calculation or comparison of size!
I'm seeing that now. Can anyone give me a push? :flushed:
 

pc1966

Arms
Esteemed
We in the UK used to use SWG, also wires would be given by strands/diameter (e.g. 3/0.029 for 3 strands of 0.029" diameter each, about 1.3mm2 CAS typically for light circuits, etc).

These days it is all the CSA that is specified, which helps a lot for sizing circuits!
 

Julie.

Arms
Esteemed
IEC 60364-5-54 states that phase conductors 16mm2 and smaller require a CPC of the same size, over 16 to 35mm2 a 16mm2 CPC and over 35mm2 a half size CPC is required.

My questions is why am I seeing catalogs with harmonized twin and earth with reduced size CPCs over 2.5mm2? And why doesn't the half size rule kick in when wire is over 4mm2 instead of 16mm2?
It doesn't - the cross sectional area is determined by calculation in accordance with 543.1.3, however if you don't want to calculate it then you can refer to 543.1.4 and table 54.7 in which case your summary is correct.

Did you just look at the table rather than reading the standard?

BTW IEC 60364-5-54 is chapter 54 in BS7671 other than the 9 clearly marked exceptions
 

pc1966

Arms
Esteemed
In reality few electricians have to use the adiabatic equation (though they should know how to) as the IET's On Site Guide has some useful tables that incorporate the information for circuit design. For example this table is for BS88 fuses and shows the maximum Zs values for different CPC sizes:
OSG-example_table.jpeg
For example, if you have 10mm T&E cable with a 4mm CPC used as a sub-main feed so you could allow 5s disconnection, you might have a 63A fuse for short circuit protection only, and then the downstream DB can use a mix of MCBs up to 32A in order to provide overload protection with a reasonable chance of selectivity. Looking at the above table you see you max measured Zs is 0.49 ohms, so your final test at the nice new DB would be to confirm this is met.

Also you see the value is 0.62 ohms in all the larger CPC sizes - they are time-limited for the fuse action, where as at 4mm it is adiabatically limited (hence lower Zs for a shorter fault disconnection time).
 

Gavin John Hyde

-
Arms
Esteemed
slight variation on the theme, I had a roll of twin and earth recently and the cpc was insulated in green/yellow, made a change... I checked and turns out this is apparently standard in Ireland. suppliers had received wrong pallet and not realised. i think if it was put on sale over here it would sale. I would buy it as it saves sleeving.
 
Some people always say non insulated CPC is safer/better because if there's a break in insulation or nail hammered in or something it will come into contact with the CPC easier, although I don't think this is in any official books you hear it alot.
 

pc1966

Arms
Esteemed
Some people always say non insulated CPC is safer/better because if there's a break in insulation or nail hammered in or something it will come into contact with the CPC easier, although I don't think this is in any official books you hear it alot.
That might be a factor, but I suspect it was originally driven by the desire to save cost of extra PVC and smaller overall size of cable to make installation easier.
 
and what's the name of the IEC publication? is it free? or where can you buy it?

what country puts in the most input to the IEC regulations?
 

Julie.

Arms
Esteemed
and what's the name of the IEC publication? is it free? or where can you buy it?

what country puts in the most input to the IEC regulations?
and what's the name of the IEC publication? is it free? or where can you buy it?

what country puts in the most input to the IEC regulations?
IEC 60364-5-54:2011
Low-voltage electrical installations - Part 5-54: Selection and erection of electrical equipment - Earthing arrangements and protective conductors

Not free - Don't know the cost - I just buy the UK version which includes all sections and is around £76 - amazon, IET... loads of places.

Most of europe - UK is a big contributor
 
IEC 60364-5-54:2011
Low-voltage electrical installations - Part 5-54: Selection and erection of electrical equipment - Earthing arrangements and protective conductors

Not free - Don't know the cost - I just buy the UK version which includes all sections and is around £76 - amazon, IET... loads of places.

Most of europe - UK is a big contributor
Thanks so the IEC is broken down into quite small publications where as BS7671 includes the whole lot in one publication.
 
Last edited: