Discuss Twin and earth used as meter tails in the UK Electrical Forum area at ElectriciansForums.net
it's something I've wanted to look at for some time because you often hear about sizing Earthing conductor and Tails with adiabatic
ok IF my calc is correct
S = √580²*5
------------ = 9.07 - 10mm
143
and
t = 143²*10²
-------------- = 6.08 Seconds
580²
Does that look right?
It is a realistic fault current as may places will have PFC of around that, but the majority of cases you are looking at the 0.4s disconnection times on a MCB for a final circuit so you are seeing much less energy.
[automerge]1592147305[/automerge]
For example, few domestic circuits will have above a 50A B-curve MCB and that has the instantaneous trip at no more than 250A
Reply to Twin and earth used as meter tails in the UK Electrical Forum area at ElectriciansForums.net
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
hi....im running cable for a split type 1.5 hp aircon....i have a roll of english 2.5 twin & earth, is this ok for the job? im running it to the...
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...