Hi. Now I'm pretty sure why this is happening, but I thought I'd check.

Just did a standard RCD test at a client, and the RCD failed the test. Did a Ramp Test to check it and it finally tripped at 100mA. It's an AC RCD, so my guess is it's an appliance or something leaking DC current high enough to swamp the RCD. I know the simple solution would be to swap it out for a Type A, but I'd like to try and find if its a faulty appliance, LED light, dimmer switch and so on, as if there is a genuine earth fault, this RCD isn't going to work. My guess is the only way to do this is to methodically go round and try and unplug/isolate anything that might be inducting a DC current. The client hasn't reported any issues, I was simply there to put in an external socket (Yes I undid my work to check I hadn't caused the problem).

Any other thoughts ?
 
The RCD needs testing in isolation from all down stream circuits, to confirm that it is working correctly without other influences. Disconnect the outgoing neutral conductor and switch all breakers off, then retest.

Old fridges sometimes slow tripping times for RCDs, something to do with capacitors supposedly. Look out for N-E faults too, these can sometimes blind RCDs
 

Reply to Type AC RCD failing test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

i have faild napit annual assessment with silly mistake of using on consumer unit type AC rcd instead of Type A rcd. i bought type A rcd but they...
Replies
6
Views
766
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
321
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
741
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
913
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock