Hi all, been asked to quote for putting in underfloor heating, but have never done it before. Whats the ' standard way' of wiring them in ?

Have checked some online ones and they are around 300W , Ib of around 1.5 amp , so can fuse spur off ring ? or best dedicate circuit ?

Wattage prob larger with area ? so larger Ib ?

Many thanks all

EDIT : 200W/M sqaured. , so eg: 20m square = 4 kW , .... 17A , dedicate 2.5mm 20A mcb ?

Thanks
 
Last edited by a moderator:
Usually full fitting instructions are supplied mate, the ones I've fitted have been on their own radial in plush new builds but I guess you could spur off an RFC
 
Not difficult then i take it ? ...would prob rather run its own radial, any special instructions i should know before making a big boo boo ? lol
 
Fitted a few of these. You need to make sure you get exactly the right size for the area as it can be hard to loose the excess.

I would always try and put them on a seperate circuit if you can.

Yes, the larger the area, the larger your design current.

Obviously you've seen you can get differerent wattage/sq m mats.


Used this company: Electric Underfloor Heating | Underfloor Heating Kits and Systems and no complaints.

300w sounds like a pretty small system, I think the last one I did was 650w and that wasn't big!

Edit: I got a fancy stat, the one with the Neon blue background - Absolute S**t of an accessory to fit, It fills a 47mm box and the teminals are on the underside of it. Just to make you aware!
 
Last edited by a moderator:
i1v seen some of your posts before dai.....so whats up here?.....why not fuse it down ....of a ring (if thats whats available localy)......and if inside a bathroom etc......then FCU it outside the special location............
 
many thanks ! :-)

The customer has told me he already bought the kit , ( haven seen it yet mind ) , but you know how it is when youve never done something before. lol, god bless this forum !!! :-D

Yeah id rather it have its own circiut, have they all got a floor probe then i take it ? ....when you did them did you advice the undermatts etc ?
 
''i1v seen some of your posts before dai.....so whats up here?.....why not fuse it down ....of a ring (if thats whats available localy)......and if inside a bathroom etc......then FCU it outside the special location............ ''


PMSL ! is that a dig :-/ lol
 
The stats i'v used give you the choice of either Floor probe, air temp or a combination of the both. Never used the single wire kits, so couldn't comment on them.

Rich
 
Lol, sweet.

I just like to get advice from experienced lads prior to diving into stuff ive never done before. :-D ..
better keep me gob shut then ant i....never fitted one of these mysen`but looking at the max current demand is what spurred me to spurr it...(fused down of course).......:tounge_smile:
 
How soon after fitting is it going to be covered (tiled?)? If it's to be a while, I'd suggest a bit of latex floor levelling to protect the element (that'll mean you'll need to plug all the holes though ;)).
 
Had a text of the guy and he was hoping for it to be done tomo morn for less than £20 ! HA HA HA HA , ....think ill have a lie in ta. lol
 
However thanks to all for all your help and advice ! ,....once again the guys here are more than helpful :-D
 