Hello again everyone. Sorry, I still have a problem with this. The fault before was because the load was too big. if you go back and read the posts before you will find that there is a 16a controller switching a huge load which is about 46 amps. It is wired in 2.5mm cable and on a 20amp breaker (not done by me I have more than a passing grasp of ohms law! am remedying the problem although wish i wasnt now!!)
So a contactor looked like an idea to take the weight of the switching load (assuming the 16a quoted on the breaker is a switching load?!) but the problem is that it is wired in 2.5mm cable so, before i let client know that this is the last option, is there anything else I can try. i cant think of anything else to be honest but to wire it in bigger cable and either use a contactor or put more controllers in (there were three heating mats hooked up to one before)
Thank you all for help so far
Ed
So a contactor looked like an idea to take the weight of the switching load (assuming the 16a quoted on the breaker is a switching load?!) but the problem is that it is wired in 2.5mm cable so, before i let client know that this is the last option, is there anything else I can try. i cant think of anything else to be honest but to wire it in bigger cable and either use a contactor or put more controllers in (there were three heating mats hooked up to one before)
Thank you all for help so far
Ed