Hello again everyone. Sorry, I still have a problem with this. The fault before was because the load was too big. if you go back and read the posts before you will find that there is a 16a controller switching a huge load which is about 46 amps. It is wired in 2.5mm cable and on a 20amp breaker (not done by me I have more than a passing grasp of ohms law! am remedying the problem although wish i wasnt now!!)

So a contactor looked like an idea to take the weight of the switching load (assuming the 16a quoted on the breaker is a switching load?!) but the problem is that it is wired in 2.5mm cable so, before i let client know that this is the last option, is there anything else I can try. i cant think of anything else to be honest but to wire it in bigger cable and either use a contactor or put more controllers in (there were three heating mats hooked up to one before)

Thank you all for help so far

Ed
 
ED

you really need to explain more or find your original thread and continue there

Note electric under floor heating at 200w per meter at 10 meter square will equal how many amps ?
I have only ever connected 2 x 10 meter mats,
Where have you got this massive load from ?????
 
Hi there, if you read back to the beginning it should(!) explain. They are heating a massive room on underfloor alone (I have advised against this) using four mats - all around 24 ohms(ish for sake of argument) They had all four mats on one 16a controller (!!) and it kept tripping out (it was also spurred off the ring - bloody hell!) so the spark who was before me left one mat on the spur and took the other three and put them on one controller on its own breaker (20a using 2.5mm T&E) - surprise surprise the controller burned out and i have been trying to sort it. Last option is to advise rewiring the system and for now temporarily putting one mat on the controller in question and leaving the other two unused for now.

As i said contactor looked like a plan but still have problem of cable and breaker being too small.

Thoughts?!
 
Ed my fault, just browsed back (but not read 100%)

Are all the mats run back to the same location ?
 
I make it about 11 m2 per mat if using the 200w/m ones, anyway if you want to use one controller, you could switch a four pole contactor, main feed from cu would need upgrading to poss a 10mm cable, just wondering if it could be ran on four x 2.5mm radials on 16m mcb's?
 
Will there's no space at the board! Was thinking standalone contactor (between stat and mats right?) but in any case needs new cable
 
Going to have to uprate the cable then and use a contactor. Control circuit for controller and contactor will need fusing down though
 
Will can you expand mate. I.e verbal block diagram!! E.g breaker, big cable, stat, conractor, mats etc with fusing down explained in there too. Thanks mate!!
 
Ok, cable and breaker size will need checking but, 50 amp mcb in original cu, 10mm twin and earth cable to near ontoller, you'll need somewhere to box this in, 4 pole contactor in enclosure, 10mm cable to input terminals linked to all 4, 4 lives to mats connected to output terminals, neutrals all connected together.
run small length of 2.5mm cable from input terminal on contactor to fused spur, neutral to fused spur from same neutral that connects the matts.
1.0mm cable from fused spur to control power in, output from controller to coil in contactor (a1and a2)
3 amp fuse in spur.
whats anyone else think?
 
This will only work if the controller is either on or off. Some control the power to the mat via pulse width modulation. Therefore this won't work with them.
 