A bit of guidance required, am down to wire up a central heating system along with underfloor heating( ufh is made by John guest) plumber has left me with a heating wiring centre and also an 8 zone underfloor heating panel, looks like a f/a panel. question is.... Do I need the wiring centre or can I just do it all with the Underfloor heating panel?
Any info would be great. Have done a couple of central heating before but none with this underfloor heating
 
you should need the salamander box for wireing the room stat and the pump to the panel....via the salamander box.......a double surface box with a blank front and a strip of 10 x 15A connector blocks should do it......
 
Will also need to try and seperate the boiler calls from the UFH and H/W-heating controller in case of back feeding, I use contactors.
 
Just the standard box. He should have left you with a bunch of activator heads Aswell. Then it's as simples as each room has its own stat cable which corresponds to each head ( or heads if more than one run per room). Just hope that it's all well marked up ...
 
Cheers for the advice guys, think I confused myself by looking to far into it, all sorted. Many thanks
 