Using other than “standard domestic final circuits” legally requires the installer to prove it is safe (strength and capability) typically done with design calcs. Please calculate (at the worse place, a fault fed by both legs) at one “leg” phase to (1.5mm cpc) earth, typical a fauna/rodent damage.
The reason why only large multicore (not table 4D5 flat T&E) cables are run in parallel. (Even then, parallel is usually done for ease of physical installation as it is inferior electrically), and always lugged at terminations.
The withstand of final ring circuits was no good back in the day when flat 2.5mm T&E had only a 1.0mm cpc, cpc would not always withstand phase to earth faults and would “fuse”, your 5.0mm lives to 1.5mm cpc is worst still.
Standard Flat 4D5 T&E cable final ring circuits are not electrically perfect, to install we have many extra requirements to keep the right side of things.