Just bumping a thread I started back along to get some views!!


and reposting below the text from my recent update, and a question.. Thanks!!
 
Just bumping a thread I started back along to get some views!!


and reposting below the text from my recent update, and a question.. Thanks!!
Hi again all, Thanks for all the contributions to this thread, just thought I'd post an update and another question!

I have not been able to give much attention to this but finally managed to visit the site and carry out some testing which revealed a straightforward solution - the nomenclature on the terminal box on the motor was simply incorrect, U, V & Z mixed up, when rearranged it was wired as a 'standard' setup. Good.

Now I am on to solving all the other issues and have ordered parts as the reversing contactors supplied had no interlock (mechanical or electrical) and no overload.
I have now sourced a reversing contactor arrangement that has all of those features, however I have realised that with the 4 wire setup to the single phase motor, 1 wire will bypass the contactors and be permanently connected (this could be L or N I guess as 2 of the 4 wires are permanently L & N respectively whereas the other 2 switch polarity depending on desired motor direction.) therefore also bypassing the overloads.
Question is , for a single phase motor such as this, do both L & N need to pass through the overload or just (for arguments sake and most likely) just L? . If both I guess I need to find a 4 pole overload as a standalone (not hanging off T1-T3) or put a 3 pole standalone upstream of the contactors? If only L needs to pass through I can stick with the arrangement I have.
Thoughts anyone?
Thanks!
 
It's conventional to wire 3 pole overload relays used on single phase so that the full motor current passes through each pole of the relay. This is usually done by passing the neural current through one pole of the contactor and relay, passing the live through another pair and then 'looping back' to the third pair. Whether it actually has any effect on the tripping characteristics, I have no idea.
On single phase, the live current is the same as the neutral, so there's no reason that I can see why looping back twice so that just the live goes through all three relay poles should be a problem. The only reason the neutral is fed through one pole of the relay on single phase is to get the DP switching from the associated contactor.
Someone at some time in the past produced a stand alone mounting and terminal block for a 'modern' type overload relay. I'm sure of this because I obtained and used one on a job once. Quite possibly Klockner-Mueller, since I used their contactors for years.
 
Tha
It's conventional to wire 3 pole overload relays used on single phase so that the full motor current passes through each pole of the relay. This is usually done by passing the neural current through one pole of the contactor and relay, passing the live through another pair and then 'looping back' to the third pair. Whether it actually has any effect on the tripping characteristics, I have no idea.
On single phase, the live current is the same as the neutral, so there's no reason that I can see why looping back twice so that just the live goes through all three relay poles should be a problem. The only reason the neutral is fed through one pole of the relay on single phase is to get the DP switching from the associated contactor.
Someone at some time in the past produced a stand alone mounting and terminal block for a 'modern' type overload relay. I'm sure of this because I obtained and used one on a job once. Quite possibly Klockner-Mueller, since I used their contactors for years.
Thanks for this. I am aware of the 'looping back' practice and have also used a standalone overload relay before however in this case I'm not sure it would help unless I put it upstream of the contactors. I'll explain.
The new contactor arrangement is shown in the photo and the diagram shows the 4 wire setup to the motor as supplied from the factory.
wire 1 is L bypassing contactors going to start winding
wires 2 & 3 are switched polarity for main winding
wire 4 is always N going to centrifugal switch
capacitors are permanently connected to switch and start winding.

The new contactor arrangement has overload relays fitted to outgoing terminals as per pic so if I wired it the same as the diagram the full motor current would pass through 1 or other of them depending on motor direction via the neutral conductor so they should work but of course wire 1 is permanently live to the motor and would remain so in all states unless isolated at upfront isolator I plan on fitting. I feel this is sub optimal. I could of course change the wiring to the permanent neutral (currently wire 4) being the conductor that always remains 'live' at the motor and switch all the L's through the contactors but not sure that is really that much better.
The contactors I have sourced are very cheap compared to other brands which is to satisfy budget remaining on this project and those thermal relays were the only type I could find in Chint's catalogue, also I can't seem to find a 4 pole standalone of any make to put all 4 wires through.
Can you suggest a better solution? I need to get this done now and I'm running out of ideas!!
 

Attachments

  • contactors.jpg
    contactors.jpg
    116.7 KB · Views: 14
  • diagram.jpg
    diagram.jpg
    70.3 KB · Views: 16
Whether it actually has any effect on the tripping characteristics, I have no idea.

It has a big effect in so far as it will trip after a short period of operation if current does not pass through all 3 poles if the overload. I learned this as an apprentice when I connected a single phase motor through just 2 poles of the 3 pole overload.

The overload relay also trips on imbalance of current through the poles.
 
It has a big effect in so far as it will trip after a short period of operation if current does not pass through all 3 poles if the overload. I learned this as an apprentice when I connected a single phase motor through just 2 poles of the 3 pole overload.

The overload relay also trips on imbalance of current through the poles.
so my arrangement with the 1 L wire not passing through the overload(s) won't work you reckon?
 
Can anyone link a diagram of single phase reversing contactor arrangement with overload, I can't find one anywhere and as you can see am struggling to work it out!
 
so my arrangement with the 1 L wire not passing through the overload(s) won't work you reckon?

I wouldn't have thought so as the current through the overload won't be in balance.

I don't know how it's normally done with reversing an SP motor but I'd be inclined to put an MPCB before the reversing contractors rather than use a thermal overload on the output.

Or just buy a complete reversing starter and use that
 
I don't know how it's normally done with reversing an SP motor but I'd be inclined to put an MPCB before the reversing contractors rather than use a thermal overload on the output.
this sounds like a reasonable idea , must admit I have never used one before so I'll look into it, Thanks
Or just buy a complete reversing starter and use that
couldn't find a suitable one or I would have done, anyway too late now have bought the quality Chint gear!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
The Sticks, Dorset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Update & follow up question!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
grumpyjohn01,
Last reply from
grumpyjohn01,
Replies
8
Views
237

Advert

Back
Top