NorthernLights
DIY
I would have to agree with you. Good luck
So is just getting a non surge protected power strip going to work and be safe given the fact U have RCD protection on the circuit?
I would have to agree with you. Good luck
I would have to say yes since it’s already RCD ProtectedSo is just getting a non surge protected power strip going to work and be safe given the fact U have RCD protection on the circuit?
That is an autotransformer, as it clearly says on it! But it is a good one to have, so there is nothing wrong with it as such.
The obvious things to check are the wiring of the UK 13A plug to it (making sure the L & N are the right way) if it is not a moulded plug. Also have you got a socket tester to make sure your 13A outlet(s) are wired the right way round? That is rare, but can be very dangerous as it puts the fuse in the neutral line.
Good to hear there are no serious wiring issues.However if I plug the transformer in, give it 10 seconds and then plug in the power strip, it then works fine.
Is this to do with inrush current on startup perhaps?
All new homes built or service changes will have to have SPD’s located at the main panel starting this year according to the 2020 edition of the NECIf you want a better long-term solution you could get a non-protected US distribution strip and add a UK style surge protector to the autotransformer input.
With the 18th edition of the IET wiring regulations surge protection devices (SPD) at the supply to a home became a factor to consider but I suspect very few home will have that for years to come.
That is good to hear, basically same ethos as our regulations!All new homes built or service changes will have to have SPD’s located at the main panel starting this year according to the 2020 edition of the NEC

RCD's dont like capacitors to ground.