Hi everyone, I need some advice please.

I have a number of 110v equipment from the US that I need to supply power to.

When using a step down 240 to 110 transformer when I plug in the 110v power Strip with built in Surge protection it trips the RCD on my consumer unit.

I read up on this a little and it seems this is a potentially dangerous situation.

Can someone explain how I can solve this other than having to buy all new 240v equipment?

Best wishes,

Nathan
 
That sounds odd, most likely is you are using an auto-transformer (or even some dubious electronic replacement) and not an isolating transformer (they cost more due to the extra copper needed) and somehow the power strip has enough leakage to earth to trip the RCD.

What sort of current do you need for your 110V equipment? Spending something like £70 or so on a decent site transformer might be a better option:
 
If your transformer is an autotransformer, a possible cause is that the common terminal is connected to the line conductor of the 230V input rather than neutral. Although the voltage between the output line and neutral is correct, the voltages to earth would be wrong, at 230V and 230-120=110V. The conductor at 230V from earth then triggers the surge protection which attempts to clamp what it sees as an overvoltage to earth and trips the RCD. This setup is also dangerous due to the presence of 230V on parts only insulated for 120.

Do you have a multimeter rated at least Cat II and the experience to use it safely on live mains voltage equipment?
 
Most likely your surge protected power strip has a path to ground,
not unusuall as most power filters use capacitors to ground as part of the filter.
RCD's dont like capacitors to ground.
 
If the transformer is delivering the voltage expected of the surge protection then nothing should happen.

But if (as Lucien Nunes pointed out) it is delivering not 0-110V for N-L but 120-230V instead, it might be satisfying the requirement for 110V between your L & N, but they are elevated well above 110V to Earth and the surge protection might try to stop that resulting in the RCD trip.
 
If the transformer is delivering the voltage expected of the surge protection then nothing should happen.

But if (as Lucien Nunes pointed out) it is delivering not 0-110V for N-L but 120-230V instead, it might be satisfying the requirement for 110V between your L & N, but they are elevated well above 110V to Earth and the surge protection might try to stop that resulting in the RCD trip.

Thank you.

So what is my safest and easiest solution to this problem?
 
Hi everyone, I need some advice please.

I have a number of 110v equipment from the US that I need to supply power to.

When using a step down 240 to 110 transformer when I plug in the 110v power Strip with built in Surge protection it trips the RCD on my consumer unit.

I read up on this a little and it seems this is a potentially dangerous situation.

Can someone explain how I can solve this other than having to buy all new 240v equipment?

Best wishes,

Nathan
Nathan I have one question did you bond the neutral on the secondary side of the transformer?
 
Nathan I have one question did you bond the neutral on the secondary side of the transformer?

I'm sorry but I don't understand what you mea. By this.

I've attached an image of the transformer I'm using.
 

Attachments

  • IMG_20200604_132933.jpg
    121.3 KB · Views: 17
I'm sorry but I don't understand what you mea. By this.

I've attached an image of the transformer I'm using.
When I say bonded I mean tie the neutral to the ground wire but since it is an auto transformer it should already be bonded on the inside when you plug it up. I’m sure your male plug has a ground prong
 
When I say bonded I mean tie the neutral to the ground wire but since it is an auto transformer it should already be bonded on the inside when you plug it up. I’m sure your male plug has a ground prong

Yes it's a normal 3 pin UK plug.

When I plug any of the devices I want to power directly in to the transformer it works absolutely fine. It's only when I then plug in the power strip that the RCD is tripping.

I've tried another identical power strip and the same happens with both, therefore I suspect it is because of the inbuilt surge protection?
 
That is an autotransformer, as it clearly says on it! But it is a good one to have, so there is nothing wrong with it as such.

The obvious things to check are the wiring of the UK 13A plug to it (making sure the L & N are the right way) if it is not a moulded plug. Also have you got a socket tester to make sure your 13A outlet(s) are wired the right way round? That is rare, but can be very dangerous as it puts the fuse in the neutral line.
 
Yes it's a normal 3 pin UK plug.

When I plug any of the devices I want to power directly in to the transformer it works absolutely fine. It's only when I then plug in the power strip that the RCD is tripping.

I've tried another identical power strip and the same happens with both, therefore I suspect it is because of the inbuilt surge protection?
I would have to agree with you. Good luck
 
That is an autotransformer, as it clearly says on it! But it is a good one to have, so there is nothing wrong with it as such.

The obvious things to check are the wiring of the UK 13A plug to it (making sure the L & N are the right way) if it is not a moulded plug. Also have you got a socket tester to make sure your 13A outlet(s) are wired the right way round? That is rare, but can be very dangerous as it puts the fuse in the neutral line.

Ok so it is a moulded plug on the transformer. I've checked the socket using my socket tester, all good.

I think I've discovered the issue. If the power strip is connected to the transformer when I plug it in then it trips the RCD.

However if I plug the transformer in, give it 10 seconds and then plug in the power strip, it then works fine.

Is this to do with inrush current on startup perhaps?
 
However if I plug the transformer in, give it 10 seconds and then plug in the power strip, it then works fine.

Is this to do with inrush current on startup perhaps?
Good to hear there are no serious wiring issues.

It sounds like on switch on the transformer is kicking out a short high voltage spike that is enough to exceed the power strip's L-E voltage protection, so in a sense it is doing its job, but equally it is not convenient for you!

Good to know you have a work-around for the problem!
 
If you want a better long-term solution you could get a non-protected US distribution strip and add a UK style surge protector to the autotransformer input.

With the 18th edition of the IET wiring regulations surge protection devices (SPD) at the supply to a home became a factor to consider but I suspect very few home will have that for years to come.
 

Reply to US Surge Protector trips RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may...
Replies
2
Views
1K
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
445
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
530
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello. we have had a few powercuts over past few months and am in middle of one at the moment where power has gone off a few times while DNO are...
Replies
8
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock