Hi everyone, I need some advice please.
I have a number of 110v equipment from the US that I need to supply power to.
When using a step down 240 to 110 transformer when I plug in the 110v power Strip with built in Surge protection it trips the RCD on my consumer unit.
I read up on this a little and it seems this is a potentially dangerous situation.
Can someone explain how I can solve this other than having to buy all new 240v equipment?
Best wishes,
Nathan
That sounds odd, most likely is you are using an auto-transformer (or even some dubious electronic replacement) and not an isolating transformer (they cost more due to the extra copper needed) and somehow the power strip has enough leakage to earth to trip the RCD.
What sort of current do you need for your 110V equipment? Spending something like £70 or so on a decent site transformer might be a better option:
If your transformer is an autotransformer, a possible cause is that the common terminal is connected to the line conductor of the 230V input rather than neutral. Although the voltage between the output line and neutral is correct, the voltages to earth would be wrong, at 230V and 230-120=110V. The conductor at 230V from earth then triggers the surge protection which attempts to clamp what it sees as an overvoltage to earth and trips the RCD. This setup is also dangerous due to the presence of 230V on parts only insulated for 120.
Do you have a multimeter rated at least Cat II and the experience to use it safely on live mains voltage equipment?
Most likely your surge protected power strip has a path to ground,
not unusuall as most power filters use capacitors to ground as part of the filter.
RCD's dont like capacitors to ground.
Thanks for the replies so far.
I don't have a multimeter to test the setup unfortunately.
If I just got a regular US style power strip without surge protection built in would that work?
If the transformer is delivering the voltage expected of the surge protection then nothing should happen.
But if (as Lucien Nunes pointed out) it is delivering not 0-110V for N-L but 120-230V instead, it might be satisfying the requirement for 110V between your L & N, but they are elevated well above 110V to Earth and the surge protection might try to stop that resulting in the RCD trip.
Thank you.
So what is my safest and easiest solution to this problem?
Best wishes,
Nathan
Nathan I have one question did you bond the neutral on the secondary side of the transformer?
I'm sorry but I don't understand what you mea. By this.
I've attached an image of the transformer I'm using.
When I say bonded I mean tie the neutral to the ground wire but since it is an auto transformer it should already be bonded on the inside when you plug it up. I’m sure your male plug has a ground prong
Yes it's a normal 3 pin UK plug.
When I plug any of the devices I want to power directly in to the transformer it works absolutely fine. It's only when I then plug in the power strip that the RCD is tripping.
I've tried another identical power strip and the same happens with both, therefore I suspect it is because of the inbuilt surge protection?
That is an autotransformer, as it clearly says on it! But it is a good one to have, so there is nothing wrong with it as such.
The obvious things to check are the wiring of the UK 13A plug to it (making sure the L & N are the right way) if it is not a moulded plug. Also have you got a socket tester to make sure your 13A outlet(s) are wired the right way round? That is rare, but can be very dangerous as it puts the fuse in the neutral line.
I would have to agree with you. Good luck
NorthernLights,
Lucien Nunes,