Just got here, and I'm not sure if this question will make sense to UK folks, or if there are any USA folks here at all.

Anyway: due to supply issues, I can't find any 4/0 XHHN or THHN. I'm trying to connect my meter to a 200 amp disconnect. Can I use 4/0-4/0-4/0-2/0 alumin(i)um SER cable for that connection?
 
I should add- this would entail removing the ground from the SER, since my ground is in the disconnect.
 
Just got here, and I'm not sure if this question will make sense to UK folks, or if there are any USA folks here at all.

Anyway: due to supply issues, I can't find any 4/0 XHHN or THHN. I'm trying to connect my meter to a 200 amp disconnect. Can I use 4/0-4/0-4/0-2/0 alumin(i)um SER cable for that connection?
I should add- this would entail removing the ground from the SER, since my ground is in the disconnect.
It sounds like you have a 3 phase service and yes on the aluminum wire size and aluminum is cheaper than copper. You can always use your local electrical parts house to purchase wire. You must pull a #6 wire for your equipment ground
I should add- this would entail removing the ground from the SER, since my ground is in the disconnect.
The wire size that you mentioned is fine for a 200 amp service to a single family dwelling. Coming from the meter to the first panel you want need a ground wire but you will need to install 2 ground rods at least 6 feet apart and install one #6 ground to the rods. It sounds like you have a 3 phase service since you are installing three 4/0 aluminum. You can also go to your electrical parts house to buy copper or aluminum wire.
 