Just got here, and I'm not sure if this question will make sense to UK folks, or if there are any USA folks here at all.

Anyway: due to supply issues, I can't find any 4/0 XHHN or THHN. I'm trying to connect my meter to a 200 amp disconnect. Can I use 4/0-4/0-4/0-2/0 alumin(i)um SER cable for that connection?
 
Just got here, and I'm not sure if this question will make sense to UK folks, or if there are any USA folks here at all.

Anyway: due to supply issues, I can't find any 4/0 XHHN or THHN. I'm trying to connect my meter to a 200 amp disconnect. Can I use 4/0-4/0-4/0-2/0 alumin(i)um SER cable for that connection?
I should add- this would entail removing the ground from the SER, since my ground is in the disconnect.
It sounds like you have a 3 phase service and yes on the aluminum wire size and aluminum is cheaper than copper. You can always use your local electrical parts house to purchase wire. You must pull a #6 wire for your equipment ground
I should add- this would entail removing the ground from the SER, since my ground is in the disconnect.
The wire size that you mentioned is fine for a 200 amp service to a single family dwelling. Coming from the meter to the first panel you want need a ground wire but you will need to install 2 ground rods at least 6 feet apart and install one #6 ground to the rods. It sounds like you have a 3 phase service since you are installing three 4/0 aluminum. You can also go to your electrical parts house to buy copper or aluminum wire.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
WV
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
(USA) 4/0 SER from Meter to Disconnect
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
paydaylooksee,
Last reply from
Megawatt,
Replies
2
Views
1,118

Advert

Back
Top