Hi, doing some work in a bathroom at the moment - just on the lighting circuit. Ext fan & ELV lights. As the house has no RCD protection at all I'm obliged to add it. All circuits are split between two 8way consumer units, each with main switch and MCBs. My options for adding RCD protection are either:

1. Just replace the lighting MCB with an RCBO - my preferred option, although I don't think the CU will accommodate the extra height of the RCBO.

2. Add an RCD in it's own enclosure in front of the CU which includes the lighting MCB. Not ideal as there'll be a lot more testing of the other circuits involved to avoid the risk of nuisance tripping from circuits I've not touched. Also, no other point of isolation so will have to pull the fuse (or get DNO in to isolate:rolleyes:)

3. Alternatively, I could replace the main switch with an 80A RCD, like you would see in many 16th edition CUs. I would put a MAIN SWITCH label under it.

Any reason why option 3 wouldn't be proper? It seems a bit regressive, but would be the neatest solution if the RCBO doesn't fit..
 
An RCD should not be used as a main switch. 314.2

16th edition split boards have a main switch controlling all circuits & an RCD controlling split side.
 
Last edited by a moderator:
Okay, I had a suspicion this was the case, but thanks for pointing out the relevant reg. Sure I'd seen boards where RCD was used as main switch - maybe my imagination!
Thanks a lot sintra, much appreciated.
 
In the late 80's/ early 90's a few housing developers installed CU's with an RCD as the main switch, I don't know how long it was done for, but I have seen it many, many times in properties built around that time.
 
good, you could of put the lighting circuit through an rcd spur in the fuse board cupboard (crap i know, but it would do it) but rcbo best option i would say
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Use RCD as main switch?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
Smugley,
Last reply from
elektrisien,
Replies
11
Views
10,207

Advert

Back
Top