If i have a large (or long) ring main to wire i sometimes use 4.0mm. Have one in a barn conversion to wire, only 5 sockets but total run will be around 60metres. What would use?

Ian
 
If the total enclosed area is less than 100M2 and there is no excessive load then i believe you can use 2.5 T&E. Some one who knows better will be along shortly though.
 
agree with pushrod. i think 2.5mm would be fine as long as floor area doesnt exceed 100 square metres if served by 30/32A.
 
You must also take into account the route of the cable.

More than likely lots of derating needed due to insulation etc so, personally i would choose 4mm.

Although its bigger, its actually easier to use as its stranded and not solid core.
 

Reply to Using 4.0mm T and E in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock