Hello can anybody offer some advise. 3 phase lathe being moved in factory workshop . I have to extend 10mm singles in the trunking, upon investigation found the 10mm earthing conductor for the lathe has been taken from the metal trunking. I will probably rewire the earth back to the d.b. as trunking may in time become disconnected therefore losing earth continuity to the lathe, am I doing the right thing or can I rely on the trunking as being a reliable means of earthing.
 
if the trunking is electrically continuous, i.e. measure resistance ( low ohms ) from DB to point of utilisation. then it's OK to use . however, it's no detriment to add an additional cable cpc, and would possibly reduce your R1+R2,
 
Galv trunking is permitted for use as a protective conductor

543.2.2 (vi) refers.

You would need to ensure it's suitability for use though, joints etc.
 
Yeah just check your readings, I always put bonding links on trunking when I use it for earth, however I don't think theres any requirement to do so, so if they are not in place I would just check all screws on joiners etc.

Tis very common in industrial situation, and perfectly acceptable too, often giving very good readings.
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
using metal trunking as earth
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
teejay,
Last reply from
teejay,
Replies
5
Views
4,862

Advert

Back
Top