Search the forum,
Discuss Using Type D MCB for discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I agree that some type of fuse arrangement is the best option but is the supply not single phase? I have never seen an SP&N busbar chamber.
I agree but it is a big out lay when a main switch and service terminal blocks through to switch-fuses will serve the purpose.
This was my thoughts, dual 6 way block, trunking and switch fuses to DP isolator £300 busbar chamber will double that.
I agree with the OP though that on a new install, service terminal blocks (or Henley/Isco blocks that you love them being called) :D look like shyt. If I could hide them in the trunking then might consider it but if not I'd rather weigh out on a busbar chamber. Could pick up a 100A one up for about £180...in the grand scheme of things I don't think it's that much when rewiring a big HMO.
Bus bar chamber and switch fuses...it's fit for purpose and designed for the job. Out of meter into a 100A switch disconnector, into bus bar chamber, length of trunking slotted sat on top with paxolin between, bush switch fuses on to trunking, link bus bar chamber and switch fuses with singles in the trunking, gland SWA's into the switch fuses...Job done.
I think we've been here before;)
Think the OP is trying to reinvent the wheel though :D. I can understand where the OP is coming from as he might be competing against idiots that wouldn't know what discrimination is...Let alone how to design discrimination into the installation. If its detailed properly in a quote then it shouldn't be a problem...Unless the customer just wants the cheapest quote and couldn't give a hoot about the standard/functionality of the installation...Then if I was him I'd say good riddance.
I think you are spot on,
This installation seems to fit between commercial and domestic, both industries are served well, but there is nothing in this middle ground. Lots of commercial distribution options, but in this case it’s now obvious none of the manufacturers have designed a SP board for BS88 fuses.
I challenged the wheel, come come full circle. Cheers guys.
I agree with LSK
With what I have heard in regards to the design of this job already, you have to spend some sort of money on a decent well structured submains system.
Get a Ryefield and do it properly IMO.
Would hate to see cables flapping about connected into Henley’s.
Never mind a single phase bs88 board......I recently had a 'qualified' bloke telling me that bs88 3 phase were no longer satisfactory.....'you've got to have a TP breaker because if a fuse goes you won't isolate all phases'......plonker!
I agree with LSK
In this case that's probably going a bit too far, cost wise especially. Small bb chamber and sw/fuses, as Lee says.
General way for a small block of flats.
Hi MWG - I feel your pain and don't mean to add more, but iirc the supply is 100A and it's split 5 ways, so is 5 distribution circuits with 63A ocpd right? Perhaps the rooms can run on the 32A fuse arrangement or does the supply need looking at? Apologies if you've already covered this or if I've misunderstood :)
U-Turn in progress..............
Having discounted the Ryfield board early on mainly because of cost I've come full circle. I've looked at every option, in reality 5 no. switched fuses with a quality distribution board is a similar cost to Ryfield.
Therefore design is Cut-out > Isolator > Ryfield > CU on each floor.
Seems obvious now, but needed to kick it around before I could get my head around it.
Thanks for prompts gents,
Reply to Using Type D MCB for discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Probably more of a maths problem than anything else / managing to confuse myself. I have been asked to look at energy consumption of some...
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
4K
Hi, I've got to put in an additional consumer unit into quite a large property and rather than daisy chaining them back to a single MCB in the...
4K