Hi, would like ta post a question about voltage drop in a cable. If I have a 230v single phase load of 500w with a 50 meter cable run reference method C . What would be the voltage drop in a 1.5mm2 ? From my calculations excluding pf I checked from the table the the voltage drop in mV/A/m of a 1.5mm cable which is roughly 29mV/A/m, so I did 29 x 2.17 x 50 = 3146.5 / 1000 which results in 3.14% voltage drop in cable. Am I right? Because when I use a voltage drop calculation app online it is rounding up the voltage drop to 1.43% when inserting the same parameters.
Thanks.
Good job !
Keep in mind the 29mV figure is with conductor running max temp 70C, so with a low current (and hence a lower temp) you will likely see a smaller voltage drop. You can look up what it should be for the next test :)
Reply to Voltage drop and cable size calculations. in the UK Electrical Forum area at ElectriciansForums.net
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...