philbullock122
DIY
First, I really appreciate any feedback you can provide. Its awesome to have a group of people that have a passion for this!
Our RV Park has a transformer dropping service down into three 200-amp meters (single-phase 240V service X 3). From each of these three meters, we have an emergency disconnect (3 in total), and then we daisy-chain 4/0 wire to each of our RV Pedestals. We have 6 campsite RV pedestals on each of the 3 lines (total of 18 RV pads). Each pedastal has in and out lugs, then have a 20-amp, 30-amp, and 50-amp breaker.
We are experiencing a voltage drop on only one leg. One leg (on all three services) remains fairly constant at 120V. The other leg (on all three services) drops to 118 at the emergency disconnects, and then looses voltage quickly. We are seeing 114V at the shortest run, 111V at the end of the middle run, and 103V at the end of the longest run. Again, the other leg remains constant 120V throughout the park.
We have tried to balance the amperage between the 2 phases. We have some 30-amp RVs and some 50-amp RVs. Initially we were seeing more amp draw from the bad leg. Now that we have moved some of the breakers to the other pole, we are getting a balance (within 10-amps). This has not changed the Voltage Drop.
We have tried to attribute this to something. We have cut power to individual service meters with no change. When we pull off the RVs from the service, we get less of a drop but not that much. We were told that maybe our wire was undersized or that the wire was too long, but we don't see any Voltage drop on the other leg, and we have an aluminum 4/0 URD wire running 500 LF to the furthermost set of pedestals.
The electricity company came out and told us they thought it was our problem. We did all of the wiring ourselves, so I'm working to get an electrician to come out. I'm pretty good with this stuff, so I thought I would be able to track down the problem by now.
We don't even know what to check at this point... any suggestions would be super helpful.
Also, does a 200-amp service meter drop in 200-amps total or 400-amps (i.e. 200 on each 120V leg)? The electrical disconnects have 200-amp fuses; do they need to be 100-amp fuses instead?
Our RV Park has a transformer dropping service down into three 200-amp meters (single-phase 240V service X 3). From each of these three meters, we have an emergency disconnect (3 in total), and then we daisy-chain 4/0 wire to each of our RV Pedestals. We have 6 campsite RV pedestals on each of the 3 lines (total of 18 RV pads). Each pedastal has in and out lugs, then have a 20-amp, 30-amp, and 50-amp breaker.
We are experiencing a voltage drop on only one leg. One leg (on all three services) remains fairly constant at 120V. The other leg (on all three services) drops to 118 at the emergency disconnects, and then looses voltage quickly. We are seeing 114V at the shortest run, 111V at the end of the middle run, and 103V at the end of the longest run. Again, the other leg remains constant 120V throughout the park.
We have tried to balance the amperage between the 2 phases. We have some 30-amp RVs and some 50-amp RVs. Initially we were seeing more amp draw from the bad leg. Now that we have moved some of the breakers to the other pole, we are getting a balance (within 10-amps). This has not changed the Voltage Drop.
We have tried to attribute this to something. We have cut power to individual service meters with no change. When we pull off the RVs from the service, we get less of a drop but not that much. We were told that maybe our wire was undersized or that the wire was too long, but we don't see any Voltage drop on the other leg, and we have an aluminum 4/0 URD wire running 500 LF to the furthermost set of pedestals.
The electricity company came out and told us they thought it was our problem. We did all of the wiring ourselves, so I'm working to get an electrician to come out. I'm pretty good with this stuff, so I thought I would be able to track down the problem by now.
We don't even know what to check at this point... any suggestions would be super helpful.
Also, does a 200-amp service meter drop in 200-amps total or 400-amps (i.e. 200 on each 120V leg)? The electrical disconnects have 200-amp fuses; do they need to be 100-amp fuses instead?