It is a swimming pool heat pump so I'd expect long periods of running.

Maybe:

1. Bearings are failing/have failed in compressor or its motor or both.
2. Low lub oil level in compressor.
3. High pressure fault in refrigerant circuit not detected by faulty HP pressure sensor.

All would cause comp motor to work harder and draw more current.
 
The main panel voltages are given in post #6. L3, serving the heat pump, is low at 218V, but that is a separate issue to the unaccountable drop in the heat pump circuit.

It doesn't seem clear to me whether the OP has measured that incoming voltage with the heat pump running or not.
My thoughts at the moment are that if the incoming voltage is dropping to, or near to, 197V when the heat pump is running then that will be relevant.
 
Re my #18: I forgot to add a fourth:

4. Check that water flow through the condenser ( an heat exchanger) - which transfers the heat of the hot pressurised refrigerant vapour to the circulating pool water - is not restricted or throttled by defective valves or valves not fully open. Also check that the pool pump is running at its correct speed and the pump is not restricted - is there a strainer which needs clearing/replacing? If the volumetric flow of the pool water is lower than it should be, the refrigerant in the condenser will be at a higher temperature than it is designed to be at which means a higher back pressure at the compressor outlet. The compressor will have to work harder - more amps - to pump the refrigerant into the condenser.
 
Last edited:
Don't forget starting current which may be 5 times higher on a conventional motor. The manufacturer might specify a maximum cable resistance that allows reliable starting at a certain head pressure at minimum supply volts.
 