purplemaf
Lol sorry people! I've not abandoned you honest! Just getting as much info as pos. If you've not seen yet then I'll enlighten you.
Today I found 25v on the metal studwork in 2 seperate places oon the 1st floor. Appeared to be directly energized by the lighting circuit. However once the lighting circuit was completely removed the other circuits combined brought back 7v. Af least now I have metal to test to instead of water! To experiment I put a bond to the metal work in one room which removed the 7v however it remained in another room. So this does explain why problem is upstairs only as the 2 floors are not connected with metal stud. Hunting on...
Today I found 25v on the metal studwork in 2 seperate places oon the 1st floor. Appeared to be directly energized by the lighting circuit. However once the lighting circuit was completely removed the other circuits combined brought back 7v. Af least now I have metal to test to instead of water! To experiment I put a bond to the metal work in one room which removed the 7v however it remained in another room. So this does explain why problem is upstairs only as the 2 floors are not connected with metal stud. Hunting on...