Hi,

I need to swap out a damaged 30A junction box on an existing ring main circuit and thought I'd replace it with Wago 221 connectors and a Wago box, but got a bit concerned by the multiple ratings on the sides of the connectors.

Can I simply swap out an old 30A JB with Wagos? Will it be sufficiently rated?

Thanks in advance!
 
There are two ratings printed on them because current ratings are defined in different ways by different authorities. The 20A rating is as per UL approval in North America, 32A as per IEC which is what we usually work to in the UK.

However, if the joint has to be maintenance free to BS5733, then the connectors are derated to 20A because the temperature rise has to be reduced to guarantee exceptionally long lifespan. That derating never occurs on a traditional 30A JB because it's not suitable for MF locations. Cables and accessories used in a 32A RFC must be rated at least 20A so the Wago 221 is still suitable whether MF or not.
 
Just do the connection and lob it under the floor like everyone else has been doing for the past 100 years
I expect to see that statement as an append in 19th Edition eh? ;)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
North
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
Wago 221 + box = replacement for 30A junction box?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Oldskoolskater,
Last reply from
Oldskoolskater,
Replies
3
Views
2,349

Advert