I'd regard an insulating section 100mm from the point of entry as at the point of entry. There is 100mm of extraneous CP.The chances of simultaneous contact with a conductive part are about zilch

Its under the kitchen units aswell, you would have to get under the units reach for the pipe and stick your big toe on the dishwaher at the exact point a fault occurs.
 
I'd say it possibly doesn't need bonding because it could be viewed as not being accessible. Bit of a grey area though. I'd probably just bond it if it were easy. Doubt it is though!
 
This is what I wrote on a certificate when I decided not to bond a water pipe.

"No Bonding To Water

Using guidance in section 6 of IET Guidance Note 8 (Earthing and Bonding), the requirement for bonding to the incoming water supply was checked and it was decided a bonding connection was not needed.

Using Rcp>(U0/Ib)-ZT with U0 = 230v, Ib = 10mA, ZT = 1000ohm which gives a limit of 22kohm, the continuity between the pipework (following the switch from plastic) to the MET was checked and found to be 42kohm."
 
Whats it got to do with additional protection to all circuits?

I was thinking of the point of establishing whether the pipework was extraneous or not. Haven't GN8 to hand re SparkyChicks #, but I've used 415.2.2 equation (in the past) for the lowest resistance where a piece of metal does not require bonding.
 
Thats all for the input. Just found out that the entry point has been dry lined streight over, so it can even be touched anymore. The first point of contact for the water is now the stop cock, which is after the insulated section.
 