Afternoon Gents,

Came across a nice scenario today. Water pipe comes from the street, into the kitchen through a concrete floor. 100mm of copper behind a kickboard where it comes through the concrete 300ish mm of Plastic Pipe, 100mm of copper then stop tap. 90 percent of the installation is copper. IR from disconnected MET to first 100mm of pipe is 967 Ohms, After the plastic pipe its 28K Ohms, obviously over the 23K Ohms recommended.
First time i have come across an Insulated Section (Thats not the big blue water main.)

Would you bond and why?
 
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Advertisement - Content continues below

Midwest

-
Arms
Esteemed
Not sure of your description exactly, but does the installation have additional protection to all circuits?
 

ChrisElectrical88

-
Mentor
Arms
Esteemed
  • Thread Starter Thread Starter
  • #4
Basically there is a plastic piece of pipe 300mm ish long 100mm away from the water pipes point of entry, under a kickboard so inaccessible.
Reading after the plastic pipe to the met is more than the 23 K Ohms revommended.

Im just making sure i havent missed a point in 411.3.1.2 which discribes this exact scenario.

Upstairs lights, alarm and dporbell have no additional protection
 
D

Deleted member 9648

Whats it got to do with additional protection to all circuits?
 
D

Deleted member 9648

I was referring to Midwests post, cant see the relevance of RCD protection to a main bonding query.
 
My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.
 

ChrisElectrical88

-
Mentor
Arms
Esteemed
  • Thread Starter Thread Starter
  • #9
My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.
Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding

So it actually states in the reg it concerns metal services entering the building
 
D

Deleted member 9648

My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.
The regulation states "Metallic pipes entering the building having an insulating section at the point of entry...…."
 
D

Deleted member 9648

I'd regard an insulating section 100mm from the point of entry as at the point of entry. There is 100mm of extraneous CP.The chances of simultaneous contact with a conductive part are about zilch
 
I'd regard an insulating section 100mm from the point of entry as at the point of entry. There is 100mm of extraneous CP.The chances of simultaneous contact with a conductive part are about zilch
Maybe so but 100mm away is not point of entry.
 
Aico 3000 Range
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Water bond, Insulated Section. in the Electrical Forum area at ElectriciansForums.net

Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom