C

ChrisElectrical88

Afternoon Gents,

Came across a nice scenario today. Water pipe comes from the street, into the kitchen through a concrete floor. 100mm of copper behind a kickboard where it comes through the concrete 300ish mm of Plastic Pipe, 100mm of copper then stop tap. 90 percent of the installation is copper. IR from disconnected MET to first 100mm of pipe is 967 Ohms, After the plastic pipe its 28K Ohms, obviously over the 23K Ohms recommended.
First time i have come across an Insulated Section (Thats not the big blue water main.)

Would you bond and why?
 
Basically there is a plastic piece of pipe 300mm ish long 100mm away from the water pipes point of entry, under a kickboard so inaccessible.
Reading after the plastic pipe to the met is more than the 23 K Ohms revommended.

Im just making sure i havent missed a point in 411.3.1.2 which discribes this exact scenario.

Upstairs lights, alarm and dporbell have no additional protection
 
My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.
 
My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.

Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding

So it actually states in the reg it concerns metal services entering the building
 
My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.
The regulation states "Metallic pipes entering the building having an insulating section at the point of entry...…."
 
I think the plastic should be at point of entry but only assuming.
 
So mine is a metallic pipe at the point of entry but thwn has a 300mm insulating section
 
I'd regard an insulating section 100mm from the point of entry as at the point of entry. There is 100mm of extraneous CP.The chances of simultaneous contact with a conductive part are about zilch
 
I'd regard an insulating section 100mm from the point of entry as at the point of entry. There is 100mm of extraneous CP.The chances of simultaneous contact with a conductive part are about zilch
Maybe so but 100mm away is not point of entry.
 