Afternoon Gents,

Came across a nice scenario today. Water pipe comes from the street, into the kitchen through a concrete floor. 100mm of copper behind a kickboard where it comes through the concrete 300ish mm of Plastic Pipe, 100mm of copper then stop tap. 90 percent of the installation is copper. IR from disconnected MET to first 100mm of pipe is 967 Ohms, After the plastic pipe its 28K Ohms, obviously over the 23K Ohms recommended.
First time i have come across an Insulated Section (Thats not the big blue water main.)

Would you bond and why?
 
Basically there is a plastic piece of pipe 300mm ish long 100mm away from the water pipes point of entry, under a kickboard so inaccessible.
Reading after the plastic pipe to the met is more than the 23 K Ohms revommended.

Im just making sure i havent missed a point in 411.3.1.2 which discribes this exact scenario.

Upstairs lights, alarm and dporbell have no additional protection
 
My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.
 
My understanding of that Regulation is that the incoming service pipe is plastic, yours is metal so to me that requires bonding.

Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding

So it actually states in the reg it concerns metal services entering the building
 
I'd regard an insulating section 100mm from the point of entry as at the point of entry. There is 100mm of extraneous CP.The chances of simultaneous contact with a conductive part are about zilch
 
I'd regard an insulating section 100mm from the point of entry as at the point of entry. There is 100mm of extraneous CP.The chances of simultaneous contact with a conductive part are about zilch
Maybe so but 100mm away is not point of entry.
 
I'd regard an insulating section 100mm from the point of entry as at the point of entry. There is 100mm of extraneous CP.The chances of simultaneous contact with a conductive part are about zilch

Its under the kitchen units aswell, you would have to get under the units reach for the pipe and stick your big toe on the dishwaher at the exact point a fault occurs.
 
I'd say it possibly doesn't need bonding because it could be viewed as not being accessible. Bit of a grey area though. I'd probably just bond it if it were easy. Doubt it is though!
 
This is what I wrote on a certificate when I decided not to bond a water pipe.

"No Bonding To Water

Using guidance in section 6 of IET Guidance Note 8 (Earthing and Bonding), the requirement for bonding to the incoming water supply was checked and it was decided a bonding connection was not needed.

Using Rcp>(U0/Ib)-ZT with U0 = 230v, Ib = 10mA, ZT = 1000ohm which gives a limit of 22kohm, the continuity between the pipework (following the switch from plastic) to the MET was checked and found to be 42kohm."
 

Reply to Water bond, Insulated Section. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K
Hi guys, sorry if this has been asked before. I’m currently in a flat where the tenant queried the water bonding. There’s a 6mm green and yellow...
Replies
4
Views
2K
Evening all, I'd guess that this is a common question but haven't been able to find anything on the forums regarding the 18th. Working in a shop...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock