It that the stat wunda supply with their kit? Never fitted their system myself. My mistake if so, it looks like most generic electric underfloor stats from the back.
 
  • Agree
Reactions: Grant webber
They can be set to pick up air temp or floor temp with a probe. What you have is fine to use.
 
There should be a sticker or something of the make and part No. on the control box. Is this to go onto an existing system?
 
IIRC, which is far from guaranteed these days, I fitted some 'stats similar to these a few years back. In spite of having terminals for an external thermistor, they were actually fitted with internal sensors. The terminals were fitted for a different version of the 'stat which did need an external probe.
As for connections, connect N, L and L1 on the 'stats to the corresponding terminals in the control box. I expect the N1 terminals on the 'stats are internally connected to the N terminals (check with an ohmmeter) are will be unused.
 