Any manufacturers information is probably only going to be of limited help as most of the components shown appear to have be (sloppily) installed at some point in the past and it is likely none of them are original.

As you have already worked out the circuit appears to be:
Power from the mains switch feeds the silver transformer primary, the transformer secondary is switched by the pair of operators buttons which sends extra low voltage AC to the red bridge rectifier, the DC output from the rectifier operates the solenoid actuator to trigger the press to operate.

The voltage selector was probably for selecting the input voltage to a previously removed transformer with multiple primary voltage tappings. The selector knob might also house a small fuse.
 
You can see the back of the voltage selector above the transformer, Atom press 2, picture.
Nothing connected, was probably for the original transformer now replaced with the silver one.
That's right!
Now my question? If i change the input current (cable 1&2) to single phase 220V will these components work?
 
Better to either read it off the transformer or see how the supply to is is configured.

If the machine does not have a neutral connection, the transformer must be 400V. If you are lucky, it will have an internal tapping selector to alter to 230V, under one of the silver end covers. If the machine has a neutral connection, and the transformer is connected between that and one phase, it is 230V and will work with the single-phase supply without any alteration.

If the transformer is 400V only, you have two choices. Find out what its secondary (output) voltage is and replace it with an equivalent with a 230V primary, or, rather clumsily, step the 230V up to 400V feed this one.
 
Last edited by a moderator:
A better photo of the trasformer!
 

Attachments

  • 20200422_184633.jpg
    20200422_184633.jpg
    141.3 KB · Views: 49
If there are likely to be big issues in converting from 3-phase to single you might want to look at getting a static converter to generate 3-phase from your single phase supply.
 
It's worth mentioning that a 230V transformer to do this job will not be massively expensive, but it will be important to discover the output voltage of the present one. If you are equipped to work safely on live equipment you could measure the AC voltage between terminals 1 & 2 which is the transformer supply. If it is 400V and you need to replace the transformer, then measure between terminal 12 and wire 16 with the buttons pressed, which the secondary voltage and is more likely to be 24V or similar. Then, disconnect the brown wire from terminal 6, connect your meter on AC amps between the terminal and the wire, and press the buttons to complete the circuit and confirm the secondary load current.
 
It's worth mentioning that a 230V transformer to do this job will not be massively expensive, but it will be important to discover the output voltage of the present one. If you are equipped to work safely on live equipment you could measure the AC voltage between terminals 1 & 2 which is the transformer supply. If it is 400V and you need to replace the transformer, then measure between terminal 12 and wire 16 with the buttons pressed, which the secondary voltage and is more likely to be 24V or similar. Then, disconnect the brown wire from terminal 6, connect your meter on AC amps between the terminal and the wire, and press the buttons to complete the circuit and confirm the secondary load current.
Now i am beginning to have an idea of what is happening! I will try to do the measurement with an electrician friend!
 
That is possible too, but depending on the voltage a relay might be needed because the buttons (which switch AC at the moment) might not be suitable to switch the DC. (they are on the AC input side of the rectifier for good reason). In any case, either the existing rectifier or a new diode must be connected as a discharge diode around the magnet coil. Without that, the inductive voltage spike would soon destroy the switch/relay and even the coil insulation. The existing rectifier provides this function in addition to converting AC to DC.
 
I'm wondering what it is for, DC injection braking perhaps?

In that case going from 400V delta-connection to 230V Y-connection might not be such a big deal. Going the other way would be!
 
Not sure where the term clicker derives from but I have worked in many of the Northamptonshire shoe factories where shoes are still hand made, John Lobb being an elite brand across the world. Fascinating places still using traditional methods and they all have clicker rooms where the leather is cut and graded. People who work these rooms are known as "clickers".
 
one more photo of the rectifier. Italian made!
I took some measurements
The voltage on the primary coil of the transformer is 400v.
The output of the transformer is 45v and when i press the buttons the current is 3Amp.
The magnet receives 40.5v from the rectifier!!! (is the rectifier cause this drop in the voltage?)
Inspecting the whole thing i understand how it's working!
The AC after the tranformer passes through the rectifier with the 2 buttons interfering so that only when I press them the 45v DC goes to the magnet and causes the hydraulic piston works!
 