What size cable do you use for lighting circuits?

  • 1mm

  • 1.5mm


Results are only viewable after voting.
Reaction score
36
So im a third year apprentice and should be qualified next year (whoopee). One thing has always made me curious and that is what cable size should we be using to rewire or in a new build for lighting in 2021? OF COURSE this depends on the load and how it's installed etc but in general what size cable would you use?
Out of the three people I worked with only one of them used 1mm. I kind of levitate towards that side as well and I'll explain why right now -
1mm cable can handle 8amps when surrounded all sides with thick insulation. That's 8x230 so 1804 Watts. 16amps clipped direct, that's 3680 watts. If anything we are all gonna be seeing more and more LED's with low power consumption and even if we don't... Well we could still have 26, 70 watt bulbs in one circuit if the cable is surrounded in insulation... Which it rarely is. Usually it's ran on top of the insulation anyway. That doubles too 52 when clipped direct! I know the price difference isn't that much but it all adds up.
I would love to know the cable size you qualified electricians use and maybe if you have time a little comment explaining why. Like I said I should be qualified next year and want to evaluate everyone's opinions before I go ahead and make my own decisions in the future.
 
1mm in a small domestic property. Easier to terminate and never seen thermal damage due to insulation. Installations should be designed to use materials without waste so 1.5mm in this scenario is wasteful in my opinion. Some will no doubt disagree ;)
Totally agree with ImpededLoop.
I've never seen thermal damage due to insulation either.
 
1.0mm here for most applications. however,est to snap endof cable at termination esp. if screw on cable as opposed to cage
 
With LED lights it would have to be a massive house to reach the VD limit.

Yes, you might get to the Zs limit of a MCB and I'm not very keen on relying on the RCD part to meet disconnection, but for your typical 6A B-curve it is quite a lot (don't have OSG to hand to check but will look it up later).

Hmm, an RFC for lights in 1mm....
 
With LED lights it would have to be a massive house to reach the VD limit.

Yes, you might get to the Zs limit of a MCB and I'm not very keen on relying on the RCD part to meet disconnection, but for your typical 6A B-curve it is quite a lot (don't have OSG to hand to check but will look it up later).

Hmm, an RFC for lights in 1mm....
Nah...

Combined lighting and power circuits on 16a breakers all in 1.5
 
Just checked, for 6A B-curve with 1mm (at full distributed load, very unlikely in LED case!) the OSG gives length limit as 68m, pretty big for most homes.
 
I would love for someone to make a case for 1.5mm cable as I have post this on a few places and haven't had anyone really make a good case for using 1.5 other than futureproofing.
Maybe it's inevitable that I will be using 1mm when Its my decision :) of course I will be mindful of all necessary factors though.
Thanks everyone who took the time too look things up and comment on this post. Really love that I came across this website.
 
I would love for someone to make a case for 1.5mm cable as I have post this on a few places and haven't had anyone really make a good case for using 1.5 other than futureproofing.
Maybe it's inevitable that I will be using 1mm when Its my decision :) of course I will be mindful of all necessary factors though.
Thanks everyone who took the time too look things up and comment on this post. Really love that I came across this website.
The only people that I have ever known to make a case for 1.5 have been “electricians” who say all lighting is done in 1.5 it’s the way I was shown and it is the only way.
 
The only people that I have ever known to make a case for 1.5 have been “electricians” who say all lighting is done in 1.5 it’s the way I was shown and it is the only way.

It's the norm in NI - can't explain why, but a lot of people in the trade would have a fit at the idea of wiring domestic lighting in 1mm.
 
1mm FTW, there is a stupid regulation about not using 1mm for 'power' circuits but you can still use it for lights and fans which seems to come from the bigger is better mentality.
 
I would love for someone to make a case for 1.5mm cable as I have post this on a few places and haven't had anyone really make a good case for using 1.5 other than futureproofing.
Maybe it's inevitable that I will be using 1mm when Its my decision :) of course I will be mindful of all necessary factors though.
Thanks everyone who took the time too look things up and comment on this post. Really love that I came across this website.

Ok here is one, I work both domestic and commercial, I often find commercial with 10A lighting circuits (Also see it in domestic) With more and more people piling more and more insulation into their lofts the derating factor of 0.5 could be achieved that would take it below 10A. Because of this I use 1.5mm when dealing with circuits with 10A lighting just to be safe..

Having said the bullc**p above which 1mm would be fine for most scenarios, here is the two real reasons I only use 1.5mm..

1. I don't have the space to carry around 1mm and 1.5mm T+E as well as 1mm 3core and earth and 1.5mm 3core and earth and then there is singles... so I just carry 1.5mm
2. I find 1.5mm is more resilient in a terminal, have a number of times with 1mm when you do the tug test the copper breaks because of the intents from possibly being over tightened. I don't seem to get this issue with 1.5mm

maybe if copper prices keep going up then I might change my mind but for now mainly really for space and the advantage that I don't have as much stock which is more efficient. The cost difference between 1mm and 1.5mm is not yet enough that I would bother carrying both..

Also although its seems like 68m is a long distance its surprising on a larger house how it can start to get close, 1.5mm you don't have to think about it, its also really difficult to judge how long the run is (Probably me being lazy though)... Would not dis anyone for using 1mm for lighting its just personal preference for the 2 above reasons why I use 1.5mm
 
If looking at 10A of lighting in some methods then yes 1.5mm makes sense and it is physically stronger.

But I would be astonished to see that load level in any domestic house with LED lights. You would expect to see different floors of any multi-storey building on separate circuits just to reduce the impact of a fault taking out ALL lights, so really 6A is more than enough unless its a massive hotel-size floor, etc (for LED at ~3A total that is equivalent to about 4kW of old filament lamps so about 40 traditional 100W points, say 15 rooms with two lights and a corridor with 10?).
 
Just to add to the cable length debate, 1mm T&E has R1+R2 = 36.2 ohm/km (OSG Table I1) and a 6A B-curve MCB has Zs limit of 5.87 ohm (OSG Table B6) so if we allow 0.8 ohm as your typical max TN-S Ze value the disconnection length limit is 140m (the 68m in OSG Table 7.1(i) seems to be on volt-drop).

Working backwards, the OSG gives the drop for 1mm at 44 V/A/km, if we keep the silly 3% requirement for lights even for LEDs, then it is 6.9V. If we draw the line at 140m Zs limit, then our max distributed load is 2.24A or about 500W of LEDs which is quite a lot for most domestic floor sizes.

If we decided to draw the line at a 100m reel of 1mm T&E (simple on the job test of length) then obviously Zs is fine on 6A B-curve, and the max distributed lighting load load is 3.1A or about 720W total.

Of course outside of domestic cases you might have a lot of simultaneously switched lights so your MCB limits might have to be adjusted to allow for in-rush, etc.
 
Last edited:
The only people that I have ever known to make a case for 1.5 have been “electricians” who say all lighting is done in 1.5 it’s the way I was shown and it is the only way.
Going back to my apprentice days we used to fit a lot of 500w flood security lights , sometimes 3 on the same lighting circuit , couple that with a dozen or more 50w halogen downlights etc. We started using 1.5 and 10amp mcbs because sometimes when the floods all got activated it would knock out a 6a mcb.
Other than that there was no reason to pull in 1.5 , also back then I guess the price difference was so small you could throw in 1.5 at very little extra expense.

Today with LED floods and LED lights most circuits will barely pull 1 amp , so 1mm will cover 99.9999% of modern day homes
 
You will get the odd member of the public who buys a new house, finds that some LEDs lamps have failed and replaces them with what they have brought from old home…. Your nicely calculated maximum load has suddenly trebled!
What if they do it 2 or 3 times, and the supply is only 1mm?
I know, extreme situation, but it might happen.

Not right, I know, but I’ve seen some new builds where it’s 1.5 looped to switches, and 1mm from switch to light.

You would know an unmarked switch wire when it came to second fix
 
As I write this, 18 people have replied to the poll, 7 of whom have voted for 1.5mm. I would love to know their reasons for using 1.5mm as standard?
 
As I write this, 18 people have replied to the poll, 7 of whom have voted for 1.5mm. I would love to know their reasons for using 1.5mm as standard?
There is absolutely no reason to use 1.5 for a standard lighting circuit , it is just old habit

you would only ever use 1.5 for NON standard lighting , like as I mention before a massive fooking house with crazy long lighting circuits or if you picked up a load of old 500w halogen lights from the boot sale and were hell bent on using them
 

Reply to What size cable do you use for new lighting circuits? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a lighting circuit cable (1mm) powering a telescope (12 volts) in an observatory total draw 84 watts drawn from a transformer. There is a 6...
Replies
4
Views
287
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
746
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
582
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
478
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock