I have made sure I wired my shed on a new circuit coming from CU (with RCD). I did this because I felt sure I read somewhere in the regs that it needs to be on its own circuit. I know this will be a job that I get asked to do sooner or later and the question I will get asked is 'can I just take the power from a spur off a socket?'.

My questions are:

1. Where in the regs does it say a shed/garage etc needs to be on its own circuit?
2. What is wrong with taking a (one) fused spur from a socket to supply shed? Is this against the regs?

I would rather create a new circuit as you never know what will get added in the shed at a later date, but where is it in the regs, I want to read it!!

Thanks all..
 
Yes, you can supply a shed via a FCU on a socket circuit. Only issue will be the 13A limit on the supply, so a separate distribution circuit is preferred where possible.

Edit: provided the circuit isn't already excessively loaded.
 
Hello all,

I have made sure I wired my shed on a new circuit coming from CU (with RCD). I did this because I felt sure I read somewhere in the regs that it needs to be on its own circuit. I know this will be a job that I get asked to do sooner or later and the question I will get asked is 'can I just take the power from a spur off a socket?'.

My questions are:

1. Where in the regs does it say a shed/garage etc needs to be on its own circuit?
2. What is wrong with taking a (one) fused spur from a socket to supply shed? Is this against the regs?

I would rather create a new circuit as you never know what will get added in the shed at a later date, but where is it in the regs, I want to read it!!

Thanks all..
why would 2 be against the regs?...its a spur....fused down because theres likely to be more than one double outlet from it=26A.....
 
hhd, as the other guys have already said, there's nothing wrong with taking it off an existing rfc, provided that it's RCD protected, suitable, etc. It's just up to you to determine whether 13A is adequate for the customer's needs, and as said, would that impact the existing circuit...
 
I would rather create a new circuit as you never know what will get added in the shed at a later date, but where is it in the regs, I want to read it!!

Why would you think that there would be something in the Reg's specific to supplying a SHED??
 
Why would you think that there would be something in the Reg's specific to supplying a SHED??

just using shed as generic term for building ouside.

=======

Thanks guys,

I just cant help thinking I read somewhere it should be a new circuit from the CU, perhaps it just said 'preferably or advisable', or perhaps I just dreamt the whole thing!

Yes, your reasons all make perfect sense, its just sometimes the regs dont always go along with sense so I just wanted to be 100% sure there were no contraindications to using a fused spur to supply a shed/outhouse etc. Obviously if it was to heat a jacuzi whilst using 3 power saws and mowing the lawn I would insist on a new circuit :smile5:

Thanks as usual to your sound advice.
 
just using shed as generic term for building ouside.

=======

Thanks guys,

I just cant help thinking I read somewhere it should be a new circuit from the CU, perhaps it just said 'preferably or advisable', or perhaps I just dreamt the whole thing!

Yes, your reasons all make perfect sense, its just sometimes the regs dont always go along with sense so I just wanted to be 100% sure there were no contraindications to using a fused spur to supply a shed/outhouse etc. Obviously if it was to heat a jacuzi whilst using 3 power saws and mowing the lawn I would insist on a new circuit :smile5:

Thanks as usual to your sound advice.
theres such a thing as `future proofing` as well though hippy.....so if its convenient to run a dedicated sub now...then do it....as you may only have to disrupt the garden in future if you dont...(think lifting flags and digging up lawns/garden stuff)...
 
My only comment is that I would always advise DP isolation on the circuit before the cable goes outside, whether its to a shed or lighting. Makes fault finding easier and this way the client can switch off the circuit in the event of nuiscance tripping and "eliminate" the outside circuit(s) easily.
 