Just looking at a CU change on a TT. I'd like to put a 100mA S type RCD before the CU. Is a 2 way (4 spaces) amd 3 metal board my only option? Its a bit big!

Have you investigated whether PME is available?
Pretty rare that it's not these days and I'd go for that every time over a TT.
 
you could enclose it in this:

depositphotos_6532539-Safe-in-stainless-steel.-Bank-Vault..jpgtotally fireproof.
, vandal proof, and Electrical Trainee resisatnt.
 
Pathetic. I know some guys who can get into that no problem, over the course of a bank holiday weekend.
Although they are a bit ill-disposed at the mo.
 
Last edited:
Have you investigated whether PME is available?
Pretty rare that it's not these days and I'd go for that every time over a TT.

No I haven't. What sort of price do they charge? Do they charge? Expect it varies between DNO's?
 
http://youtu.be/uOypkkgTEB0

look at 4 minutes into this video. It shows an insulated enclosure for an S type RCCB. so Wylex infer this is acceptable but as stated earlier, if you contact their technical department they will not confirm that it is actually compliant. Odd to show an installation design and then not actually make a firm statement on whether or not it actually complies.
 