hi all, just need 2 pick some brains over earthing. Have come to a secxond fix this week, and have to hook up this fancy whirlpool tub. The whole job is nearly complete, builders are just finishing and making good, when i realise the tub has a fly green and yellow on one of the motors. Obviously this must be to bond the jet outlets etc, but where would be the best place to bond???

Main water & gas bonding in place and all circuits on 17th ed board, so no green and yellow was run into the bathroom. Should bond to the taps, although this is that crap flexible hosing stuff, or should i just connect it to the baths junction box/ circuit box; but why hasn't this been done already???

As i sed, they have made good, so can't go drilling and knocking. Appreciate all comments, event those sacastic ones. Many thanks......
 
Find the most accesible circuit in the bathroom

Please ignore the preceeding reply. if all water supply rads and taps is in plastic then there is no req for supp bonding as the conduction is bconsidered to be by the Cu not the H2O
 
Last edited:
If the water is supplied by plastic pipe there is no need to supp bond because any metal pipe work showing above the floor becomes plastic below the floor and is deemed to be isolated from extaeneous conductive parts of the building. EG the towel rail might be nice shiny chrome but if everything below the floor is plastic ther is deemed no chance of a potential diff between a tap and a towel rail therfore no need for supp bond req
 

Reply to Whirpool bath prob !!!! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Good Afternoon All, So I have a new situation to me that I cannot seem to get a definitive answer for. I trained as an electrician and did...
Replies
0
Views
725
I’ve just done an EICR on an old 2 bed flat that is wired in all metal conduit wired in singles however there are no CPC’s. The conduits are all...
Replies
10
Views
3K
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
Need some help please. Got a brain teaser for my first post. My pool pump motor cratered over 4th of July. It was working fine and started to...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock