Does anyone know why RCDs have changed in type in the 18th. Someone told me it was some5hing to do with DC faults? What type were they and what are they now?

Thanks

Spud
 
Not aware that they’ve changed.
It could be something to do with some cease to work if some types of d.c. voltage are present.
 
Not aware that they’ve changed.
It could be something to do with some cease to work if some types of d.c. voltage are present.
When I say changed in 18th I probably being a bit broad. Hager have changed their RCD type and assumed it was something to do with the 18th but prob isnt
 
Where an installation has solar panels or a car charger, there is a possibility of d.c. current leaking into the rest of the system.
Type A and AC RCDs will not work if the d.c. current is too high.
Type B RCDs are not affected by d.c. current.
 
RCDs have not changed, however.
Hager have decided to use type A RCDs in their split load boards, as well as uprating them to 100amp.
According to Hager there were a few instances last year where AC RCDs were returned to Hager due to failing to trip. They determined it was because of a high number of DC power adapters/usb charging sockets on the circuit, which creates a higher earth leakage which can also affect RCD trip times. So now they ship with type A RCDs due to better capability/ selectivity across the board. There is nothing wrong with AC type RCDs in most cases though.
Your hear different story's from the folk down the wholesalers, though im sure and some mis-informed Hager reps might get confused.

Really its down to the designer to select what type of RCD is best.
 
Last edited:
RCDs have not changed, however.
Hager have decided to use type A RCDs in their split load boards, as well as uprating them to 100amp.
According to Hager there were a few instances last year where AC RCDs were returned to Hager due to failing to trip. They determined it was because of a high number of DC power adapters/usb charging sockets on the circuit, which creates a higher earth leakage which can also affect RCD trip times. So now they ship with type A RCDs due to better capability/ selectivity across the board. There is nothing wrong with AC type RCDs in most cases though.
Your hear different story's from the folk down the wholesalers, though im sure and some mis-informed Hager reps might get confused.

Really its down to the designer to select what type of RCD is best.
A supplier asked me about 100Amp rcds due to 18th edition, i told him i was unaware of this, which i am. Does it only apply to single upfront rcd on 100A supplies not split?
 
I dont think that the RCDs have to be rated 100amps. Schneider are currently doing a dual RCD board with 2no 80amp RCD (type A) and a SPD.
 
A supplier asked me about 100Amp rcds due to 18th edition, i told him i was unaware of this, which i am. Does it only apply to single upfront rcd on 100A supplies not split?

CD9E473F-2F83-4AAF-B61E-B22C3AFB824B.png


1ECFA514-2E40-4AD5-B36F-C4D05DCE59B1.png
 