I have just popped out to a frustrated customer who has had intermittent tripping of a 30mA RCD for years, on average 5 - 10 x p/month. It used to be 10 x p/month a year ago, now it is around 5 times p/month. This is a dual RCD board (Harok??) with 2 socket circuits and 2 lighting circuits on the affected side. There is alot of electronic equipment plugged in.

I did a x5 and x1 test (at a socket). The RCD tripped but the tester just came up with 'trp' meaning it tripped too quickly for a reading. The ramp test did the same. I then tested at the RCD and it tested as 24mA and 19ms. The customer was adamant the RCD was 'too sensitive', but the above tests seem to show it is not (although 19ms is a little quick).

Global IR results showed 1.7Mohm N-E.

I clamped the Main earth (TNCS). It jumped up to 26mA for <1s and then stayed at around 3mA. It did this every time I tested. It is a poor quality earth clamp meter. He had switched off most of his electronic equipment when I tested, but not unplugged, therefore N still attached.

He just wants me to change the board, and throw money at me as he is so fed up. However, that's likely not going to solve the problem, hence having a chat with you guys.

Would an RCBO board help? I.e if it is a build up of earth leakage this option would help. It wouldn't help if all the earth leakage was just on one circuit though.

Do you think it is natural earth leakage from electronic equipment? If so, what is the solution? I'm not too sure how to test each item of equipment for earth leakage.

Perhaps it is something else. Is 19mS too quick to trip (I think it is on the low side, but not abnormally low)?

Perhaps an intermittent fault which didn't show up when I tested. However, he said it had tripped just before I came and tested.

My instinct is on accumulated earth leakage, but again I'm unsure of the solution or testing for this.

Cheers all ?
 
As @telectrix said, go for an RCBO board. It will probably fix it for good if it is related to accumulated leakage. Even if it is not fixing an underlying problem, at least you will know which of the 4 circuits is responsible which would speed fault investigation, and the annoyance value will be significantly less.

Also gives them an SPD, and while many are sceptical of their benefits I certainly think we will see more issues of cheap & nasty consumer electronics failing on smaller surges that simple or well-designed electronics would laugh off.

Something like the Fusebox RCBO board with SPD is not that expensive, total cost would be dominated by your work.
 
Also maybe ramp test at the RCD with one circuit off at a time? See if the "trp" is only with one circuit OFF.
As above, if the customer wants a new board then an RCBO board is a step in the right direction anyway. A Fusebox board would be ideal.
 
Testing for cumulative leakage is best done by clamping the line and neutral tails together, not the main earthing conductor, as there can be all sorts of stray currents flowing in the main earth.

Is that accurate when you clamp the 2 together, I presume it is

Obviously main earth's may have leakage from non RCD protected circuits so isn't likely accurate
 
Yes it's basically simulating what the RCD senses - an imbalance between line and neutral. Probably even better to clamp the cables of the RCD in question if it's a split load board.
 
I clamped the Main earth (TNCS). It jumped up to 26mA for <1s and then stayed at around 3mA. It did this every time I tested. It is a poor quality earth clamp meter. He had switched off most of his electronic equipment when I tested, but not unplugged, therefore N still attached.
Clamping the main earth is not an accurate method of assessing the earth leakage you need to clamp the live and neutral feeding the RCD together and any inbalance will be read by the clampmeter as the true earth leakage as this will include any parallel earth paths
 
Many thanks for all the replies.
I've gone with the RCBO board and will report back when it's fitted ?
 
Hopefully , you haven't a massive number of circuits on the affected side

The lighting may not be involved and it could depend on the balance of leakage on the 2 socket circuits if this is an issue

Some testing may be prudent as posters advised
 