Hi Lucian,

I totally agree with you on this outlet that has no neutral.
Connecting neutral to ground is only done at the main panel, and not allowed in any other place.

I will remove the receptacle and put a blank cover on this outlet. The ROMEX cable from the switch box above to this outlet box is not connected to anything at present time. Can I leave it this way or must do something about this cable ?

Ideally, I could remove this cable, remove the outlet box, do some drywall work to patch up the outlet opening then paint it. This is much more work but still within my DIY abilities.

I have removed more than a dozen low power devices embedded in the walls (Radio , Intercom, Alarm systems, their power adapters, alarm sensors) of this home and patched up the wall openings when my home went thru completely remodeling / painting, etc ... 9 months ago. Those are state of the art 40 years ago and now become state of the lost art.
Just putting a blank on it will suffice.

Back in the day (10 years ago or so) the US electrical codebook (NEC) started requiring a neutral to be brought to switchboxes. Until then, we usually didn't.
 
I think what you have now is a functioning circuit that is still potentially dangerous and not code-compliant. As I understand it, the original outlet in question is running its neutral current down the ground wire of the cable to the nearby light, which is now going across your link to the other light and some unspecified route of ground wires back to the panel.

Could @Megawatt, @Maji236 or someone US-based please comment?
@Lucien all I told the OP to try and combine the neutral to the ground wire just as a test ONLY to see if it started working. By no means did I think he would leave it like that
 
Just putting a blank on it will suffice.

Back in the day (10 years ago or so) the US electrical codebook (NEC) started requiring a neutral to be brought to switchboxes. Until then, we usually didn't.
Install wire nuts on each wire for safety and install a blank cover on it
 
all I told the OP to try and combine the neutral to the ground wire just as a test ONLY
I didn't mean that was your suggestion. There was no neutral from the beginning, the outlet was already using the ground wire as neutral, and we had already proven that the connection was broken. I was curious as to whether a combined neutral/ground conductor had ever been acceptable to the NEC for grounding ordinary outlet circuits in domestic wiring, excluding known special situations such as the 10-30 dryer outlet.
 
I didn't mean that was your suggestion. There was no neutral from the beginning, the outlet was already using the ground wire as neutral, and we had already proven that the connection was broken. I was curious as to whether a combined neutral/ground conductor had ever been acceptable to the NEC for grounding ordinary outlet circuits in domestic wiring, excluding known special situations such as the 10-30 dryer outlet.
@Lucien you nailed it and yes at one time the grounding conductor was always used on dryers, and stoves. Of course now if you work on a house you have to pull new wire to them 2 appliances only if they buy new ones. I was under a house one day and was installing new wire for a stove they had bought and after disconnecting the wires and cut what I was thought was the stoves old cable with my ratchet cutters and POP, I had cut the dryer cable. He got his dryer rewired for free. ?
 
Gentlemen, thank you for this riveting post. I read every response and was at the edge of my seat working through it post by post with yall
 